Discuss 24V dc lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

mhar

-
Esteemed
Arms
Reaction score
414
I am having a flat roof constructed with solar panels over. As it is a cold, vented flat roof I will be having 175mm of Cellotex insulation immediately above the ceilings which I am reluctant to dig into to fit downlights (which I have never been the world's biggest fan of anyway). My thoughts are to have plaster in led profile and led ctt tape which I have used to good effect in the past.

In order to avoid bulky power supplies everywhere would it be practical to run a 24V dc circuit (powered by two batteries in series with a voltage regulator to maintain the output). The dimmers and ctt changers that I have fitted in the past have been separate items after the driver. I intend to use a fair bit of tape for lighting.

Has anyone done this before or are there good reasons why not! Thoughts and practicalities would be appreciated
 
The wiring can all run at 24V, starting from a PSU and distribution point somewhere convenient. Beware voltage drop, which is 100 times more severe at 24V than 240 (10 times the current, but 10 times less total volts to lose) and ensure that the OCPD on the 24V side will work (although like dimmers, the PWM controllers rather scramble any attempt to calculate fault current which will be tiny)

I'm not sure about the significance or function of the batteries; is this part of a UPS scheme?
 
Thanks for the reply. I have access to EnerSys Powersafe SBS C11F batteries removed from ups systems, they have about 10 years of anticipated life in them. Converting from dc from solar pv to ac for a power supply which then converts back to dc seems unecessary. Also the cost of the psu is a consideration as is the bulk of the things, concealing a number of these would be an issue especially if I was running a standard 240V ac circuit and required multiple drivers.
I note your comments on volt drop. Luckily I am unlikely to have any run much over 10m. I envisaged using 3182Y flex and each circuit going back to a vehicle type fusing system.
These are initial thoughts, if there is a good reason not to have a dc circuit then I won't, I would be intersted to discover why this isn't done though. Since the adoption of led lighting it seems sensible to me though
 
Thanks for the reply. I have access to EnerSys Powersafe SBS C11F batteries removed from ups systems, they have about 10 years of anticipated life in them. Converting from dc from solar pv to ac for a power supply which then converts back to dc seems unecessary. Also the cost of the psu is a consideration as is the bulk of the things, concealing a number of these would be an issue especially if I was running a standard 240V ac circuit and required multiple drivers.
I note your comments on volt drop. Luckily I am unlikely to have any run much over 10m. I envisaged using 3182Y flex and each circuit going back to a vehicle type fusing system.
These are initial thoughts, if there is a good reason not to have a dc circuit then I won't, I would be intersted to discover why this isn't done though. Since the adoption of led lighting it seems sensible to me though

The losses in your regulator may well be nearly as much as the losses in the LED driver that steps 240VAC down.
 

Reply to 24V dc lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
608
Hi Guys, Looking for a bit of advice for my kids power wheel car. I have a 24v to 12v converter which I need to use for the steering motor as...
Replies
9
Views
729
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock