Hi everyone,

I have a particular job visited this morning, that on all circuits, at each point, i got a reading off around 25ohms for a earth fault loop impedance test(zs).

I then thought to do the same at the DB for those circuits. Again, same reading was obtained.

I then turned off the whole installation, to obtain a Ze with the incoming earth disconnected. Same value obtained.

Can anyone shed any light to what may be going on here, I suspect an issue on the DNO side of things?

Thanks in advance.

Nick Sage
 
A slightly embarrassing admission but after a long day of fault chasing, tripping sockets, not Ze related, I reinstated the circuit and on my way out did a quick Zs and got a similar double digit Zs.

Chased it all the way to the MET and had the same result from the bus bar camber to the MET.

As I could physically see the main earth all the way to the MET I just assumed it was a poor incoming earth (TNS)and called the DNO.

Hung round and they turned up within the hour, popped the head off the service head and showed a Ze of 0.12 Ohms.

Put the main earth back on the MET bar and back up to double digits, turned out to be a corroded MET bar. Not green and crusty just a dull brown colour.

Unbolted all the various earth's and bondings and took some emery cloth to the bar, coupled it all back up and Zs at the bus bar chamber was 0.12Ohms.

Never seen it before or since, very weird.
 
If you're right about TN-S then this needs urgently looking at. Don't be afraid to call the DNO, better safe than sorry.

How much (if any) of the installation has RCD protection?
A fault to earth would give a fault current of 9 amps, and without RCD protection the only thing that might trip is lighting, and then only after around 50 minutes! So this is potentially quite a dangerous situation.

Do you have any photos?
 
A slightly embarrassing admission but after a long day of fault chasing, tripping sockets, not Ze related, I reinstated the circuit and on my way out did a quick Zs and got a similar double digit Zs.

Chased it all the way to the MET and had the same result from the bus bar camber to the MET.

As I could physically see the main earth all the way to the MET I just assumed it was a poor incoming earth (TNS)and called the DNO.

Hung round and they turned up within the hour, popped the head off the service head and showed a Ze of 0.12 Ohms.

Put the main earth back on the MET bar and back up to double digits, turned out to be a corroded MET bar. Not green and crusty just a dull brown colour.

Unbolted all the various earth's and bondings and took some emery cloth to the bar, coupled it all back up and Zs at the bus bar chamber was 0.12Ohms.

Never seen it before or since, very weird.
Bit confused. Were you working alongside the OP, or is this a separate thread to the OP's?
 

Reply to 25 ohms Zdb + same reading for all circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Just completed an EICR which had an Unsatisfactory Report done earlier in the year by another Spark, i have a copy of the report and he's put the...
Replies
11
Views
4K
Hi I bought a holiday lodge last month and decided to test the circuits to see how they measured. The lodge itself is fed from a central point in...
Replies
30
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock