Good morning Guys















Looking for some advice with regard to a current job.

Building company I'm doing work for are installing Electric heating on a property.

Customer has no access to Gas so there are 2x 9kW Electric boilers being installed. (Plumbers and Builders recommendation).The incoming supply was initially 60amps

I made customer and company aware that the incoming supply wasn't big enough ( Electric shower and electric Cooker currently in place aswell). I advised that they would have to upgrade the fuse but that the maximum was 100 Amp for a domestic property.

I was then told that the fuse was upgraded and the works have now begun. The main Fuse sticker is showing 100Amp.(So I'm presuming that's what been installed) When I arrived on site I noticed the boilers were 9kW and made a calculation of around 78 Amps on full load. The manufacturer informed me both boilers won't run together initially at same time. Only one will come on initially and then once heat has reached the other will kick in.

So my question is, I'm a bit worried about the maximum demand. And where do I stand in terms of the installer.

Has anyone been on this situation before

Many Thanks
 
As in, electric system boilers? Personally I think this would be fine on 2no. 32A radials (yes, I know the maths says 39A....) however, what you could do instead would be to install a 63A feed (I'm saying 63A because (a) I think that'll be fine and (b) you'll struggle to get more than a 63A MCB for a domestic board) to a simple twin module CU that's sited with the boilers (use a four way and you've got space for all your control circuits...) and have two local 40A breakers at that point.

It's always worth remembering in these situations that a 100A 88:2 or whatever it may be will sit at 110A for...... almost forever. So whilst it can be frowned upon as not entirely legit to the letter of our dictat, at an engineering level it's fine unless you expect people to actually be in the shower, boiling four pans on the hob, kettle on for a coffee AND setting the heating to 30degs, simultaneously for 20hrs. That's why we have the principal of diversity. You also have to consider that when the DNO came along and upgraded the supply, they didn't change the cable in the road, they just put a bigger fuse on the end of it! @Julie. will know this more than me but from memory I think the DNO's work out their own diversity as something like 8A per dwelling - it's a really low number!
 
Last edited:

Reply to 2x 9Kw Electric Boilers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My company has recently done some air source heatpumps which require DNO notification and EV chargers which also require DNO notification. On an...
Replies
8
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock