Hi I have a question hoping I can get some help. I wanted to know if there is a 400V 3 phase supply (A/A/A) terminated on the primary side of a TMD breaker can you take 2 phases from the secondary side of the breaker (A/A) to create a 400V supply only excluding E/N and use to power up your load/equipment.
 
Probably not, but it really comes down to exactly what you mean by "two phase".

If you can use a floating 400V supply, say for feeding some transformer or similar isolated load, then taking any two out of the three phase L connections will deliver that.

However, if you need either a simple single-phase 400V with one side neutral (i.e. reference directly to the Earth), or if you need a proper 200V - 0V - 200V two phase supply, then the answer is no. For either of those you would need to use a transformer.
 
Probably not, but it really comes down to exactly what you mean by "two phase".

If you can use a floating 400V supply, say for feeding some transformer or similar isolated load, then taking any two out of the three phase L connections will deliver that.

However, if you need either a simple single-phase 400V with one side neutral (i.e. reference directly to the Earth), or if you need a proper 200V - 0V - 200V two phase supply, then the answer is no. For either of those you would need to use a transformer.
The intention is to create as you mentioned a 400v floating supply by using 2L phases out of the three on the secondary side of the TMD breaker. This will then be terminated on to an isolation switch then a single phase step down transformer which outputs 230V on the secondary side. My only concern is the load balance upstream to the 3 pole breaker, which is an isolation transformer feeding multiple distribution boards. My intention is not to create a major inbalance when using just two phases out of the three from the breaker.
 
My intention is not to create a major inbalance when using just two phases out of the three from the breaker.
You will create an imbalance doing this. How much of an impact it causes will depend on your load relative to the total supply, etc, and if you have more than one load so you could split them over phase-pairs.

Probably the only practical way to avoid an imbalance would be something like a 3P UPS that coverts all 3 to DC in a balanced manner and then regenerates AC from that. A few of the smaller 3P UPS (10kVA sort of region) are really single phase out for feeding IT equipment (if you check the specifications they might be something like 20A/phase but in bypass it is 60A on one phase, etc). Or old school motor-generator rotary convertors, etc, but they have other issues.
 

Reply to 3 phase 400v supply to 2 phase supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hello. How i should connect this 1 phase 2 pole 400v cooling pump? If i apply 1phase 230v and neutral it Will only growl and "spin" very very...
Replies
11
Views
683
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
576
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
993

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock