Just been asked to quote for running new supply & connecting a 3 phase cooking appliance in a small bakers. Don't really do much with 3 Phase so just a quick question.

DB has 3 phase 3 pole breaker spare and the run is around 40-45 meters away from the DB
Done a quick calc and the SWA needs to be 6mm 4 core. Whats a good isolator for the other end would you say? Also since this is fixed equipment and am i right it doesnt need to be RCD protected ?

thanks
 
i concur with your cable choice. 4mm is borderline as regard VD. i'd fit a 45A 4 pole isolator local to the cooker. RCD is not required.

edit: and a 32A MCB.
 

Reply to 3 phase Cooking Appliance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
616
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
770
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
905
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock