Discuss 3 phase machines in the UK Electrical Forum area at ElectriciansForums.net

H

Hawk

Was looking at a job where the customer wants another dishwasher same as the one that they have. The one they have has a rating plate which says 6.6kw/12.4A. It is wired in 6mm on a 40A mcb. Length of run is 10mtrs. Now I would have thought that 400x1.732=692.8
6600/692.8=9.53A therefore a 2.5mm cable on a 16A mcb should suffice. Am I missing something?
 
Was looking at a job where the customer wants another dishwasher same as the one that they have. The one they have has a rating plate which says 6.6kw/12.4A. It is wired in 6mm on a 40A mcb. Length of run is 10mtrs. Now I would have thought that 400x1.732=692.8
6600/692.8=9.53A therefore a 2.5mm cable on a 16A mcb should suffice. Am I missing something?

Three Phase Current - Simple Calculation
 
Was looking at a job where the customer wants another dishwasher same as the one that they have. The one they have has a rating plate which says 6.6kw/12.4A. It is wired in 6mm on a 40A mcb. Length of run is 10mtrs. Now I would have thought that 400x1.732=692.8
6600/692.8=9.53A therefore a 2.5mm cable on a 16A mcb should suffice. Am I missing something?

I don't know what you are trying to calculate there but if the data plate says 12.4A then that is your design current.
A 16A mcb seems appropriate.
I cannot comment on cable size as you have not provided enough information, but at a guess I'd assume 4mm until further information is provided.
 
Do you know if the supply was put in for the current dishwasher?

It may be the original installation was for a larger more powerful dishwasher.
This may have been downgraded and now they've found out it's too small and need additional capacity.
 
Do you know if the supply was put in for the current dishwasher?

It may be the original installation was for a larger more powerful dishwasher.
This may have been downgraded and now they've found out it's too small and need additional capacity.

Good old cost saving that ultimately costs more!
 
Future proof Dave! :)

What's future proof? Do you mean my estimate of 4mm? That's based on the fact that the generally default cable size for small power commercially these days is 4mm, this effectively automatically accounts for grouping, VD etc on standard small power circuits such as this.
 

Reply to 3 phase machines in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
836
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
841
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock