cmar79

Hi All, just registerd and my first post, so be gentle..
Question Regarding a Secondary 3 phase meter i installed on Friday. On Power up noticed that dial was running backwards. i tried changing 2 phases over and still running backwards, tried swapping other 2 phase over and you guessed it BACKWARDS.
Anybody any theories/answers???
:confused:
 
Hello and welcome !
What phases did you change over ? when installing 3 ph meters dont swop leading or trailing pairs instead if phase rotation is wrong swop in pairs 3+4 with 5+6 so 3 will be where 5 was and 4 will be where 6 was etc that should work or might be a duff meter check with phase rotator.
 
Hi cmar79
No start again buddy L1 pairs to L1 etc then if phase rotation is reversed only swop L2 pair with L3 pair Leading pair and N's stay the same !
Regards
Kung.
 

Reply to 3 phase meter in the Canada area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
933
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
947
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
647
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock