Hi I have a 3 phase 400v motor wired in star configuration it is controlled via a 3 pole 415v coil contactor which is switched simply via a stay put stop ... In for off Out for run.. ( Spanish design ) there is also a single phase fan connected between one phase and the star point of the motor. Got a number of these machines like this but this one.... sometimes when you release the stop button to start the motor it runs in reverse !!!!
In 50+ years in the industry Ive never seen this happen .... Any ideas?
Thanks
Dennis
 
I wonder if there is a phase missing or a faulty contactor. The missing phase possibly being replaced by the single phase motor.
 
I'm assuming that you've done all the usual supply polarity / rotation checks?
 
Agree, likely intermittent contact or connection in one phase. If the fan is disconnected it probably won't budge, but with the fan there is enough of a phase-shifted current flowing to generate a modest starting torque. Presumably it doesn't have much load at start-up?

Clamp ammeter on each line in turn to spot the one that doesn't always have load.
 

Reply to 3 phase motor reversing itself in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
672
evening all ive got a single phase AC fan motor running normally however occasionally on start up it starts in reverse. i have 4 no fans, and this...
Replies
4
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi Forum Members I have a 4 pole single phase 240VAC 315 watt motor from a central heating heating system that I think is bad. It's the room fan...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock