Discuss 3 phase power calculations. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Dear all..

May be some body can help me to explain what happened with my generator set module. At my attach picture. According to S2 = P2 + Q2 is not correct. Can some body explain it.
 

Attachments

  • IMG_20211115_113436.jpg
    377.5 KB · Views: 18
13% out does look a bit high.

You would need the meter manual, it is likely the kWh and kVarh are instantaneous, whilst the kVAh may be averaged over some time period, or all likely different periods
 
The instantaneous values of S, P and Q (kVA, kW, kVAr) add in quadrature so S² = P² + Q². But the time integrals (kVAh, kWh, kVArh) do not add in this way. The generator kVAh figure is the integral of the vector sum, not the vector sum of the integrals.
 
The instantaneous values of S, P and Q (kVA, kW, kVAr) add in quadrature so S² = P² + Q². But the time integrals (kVAh, kWh, kVArh) do not add in this way. The generator kVAh figure is the integral of the vector sum, not the vector sum of the integrals.
can you translate that into english? ?
 
Sure.

If you walk one mile east and then one mile north, you will be one mile east and one mile north of your starting point, having walked a total of two miles.
If instead you walk 1.4 miles north-east you will still arrive at the same point one mile east and one mile north of your starting point, having only walked 1.4 miles.

You cannot calculate the journey distance (kVAh) from the distance moved east (kWh) and the distance moved north (kVArh) without knowing on which bearings you travelled along the way (cos (φ))
 
Sure.

If you walk one mile east and then one mile north, you will be one mile east and one mile north of your starting point, having walked a total of two miles.
If instead you walk 1.4 miles north-east you will still arrive at the same point one mile east and one mile north of your starting point, having only walked 1.4 miles.

You cannot calculate the journey distance (kVAh) from the distance moved east (kWh) and the distance moved north (kVArh) without knowing on which bearings you travelled along the way (cos (φ))

So......that's what them pointy arrow things on vector diagrams were all about.....?
Nice one L.
Hope things are going OK, by the way.
 
It's mean triangle power can not use?

Not on the cumulative totals, only on the instantaneous value, unless the power factor is exactly constant. If the power factor changes during the counting of the totals, the hypotenuse of the 'triangle' stops being a straight line.
 

Reply to 3 phase power calculations. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
998
Hi lads 5 year safety inspection the spark put the tails back and later line 2 of the 3 phase blew blowing the box off the wall and taking out the...
Replies
81
Views
5K
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
918
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock