OP
- Reaction score
- 2
We are talking 12kw at the top end no more than that a 1kw for other bumfluffery fans main server lights etcYeah and we'd have 5 to 8 running at any one time
Discuss 3 phase problem after spark did 5 year safety inspection in the UK Electrical Forum area at ElectriciansForums.net
We are talking 12kw at the top end no more than that a 1kw for other bumfluffery fans main server lights etcYeah and we'd have 5 to 8 running at any one time
I'm not ruining your Christmas here am I mate ? More than happy to leave this till mid week if your dinners going coldOne on each socket?
I just dip in and out of here when i get a sec, i really have no further ideas, thats not a massive load if all is well, but hefty if there was a poor main switch or loose wireI'm not ruining your Christmas here am I mate ? More than happy to leave this till mid week if your dinners going cold
True there is a higher draw at start up as we need to get the building down to optimum temp and the fans on the machines work harder until we reach equilibrium but a loose wire is a disaster no matter what the load is isn't itI just dip in and out of here when i get a sec, i really have no further ideas, thats not a massive load if all is well, but hefty if there was a poor main switch or loose wire
True there is a higher draw at start up as we need to get the building down to optimum temp and the fans on the machines work harder until we reach equilibrium but a loose wire is a disaster no matter what the load is isn't it
I think we all agree on that, but as it was running when the inspector left, something happened in between, the live side of the main switch has a significantly larger hole in the top compared to the neutral, so id say its sat there loose with 50A running through it getting mighty hot followed by a bit of arcy action first before it truly ---- itselfI still maintain its nothing to do with a balanced or unbalanced 3phase load.
I do not think it is an overload (you dont get flash/bangs like that and molten copper from an overload)
IMHO Its a L - E or N 'Dead Short'
Yeah and there's a lot of breakers on our system theres breakers in the pdu there are breakers on the main board surely it would just stop working with too much power drawnI still maintain its nothing to do with a balanced or unbalanced 3phase load.
I do not think it is an overload (you dont get flash/bangs like that and molten copper from an overload)
IMHO Its a L - E or N 'Dead Short'
Good spot! It looks exactly that.Looks like the Red clamp has squashed the cable and split the insulation.
That's allowed the copper core to touch the earthed metal backplate and or the screw holding the clamp.
If it was the cable lose in the terminal or wrong side of termianl clamp it would have fizzled and overheated for a while before ultimately failing.
As Westwood, it looks like a dead short, especially with the ball of copper
Reply to 3 phase problem after spark did 5 year safety inspection in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.