Discuss 3 phase regs in proximity to swimming pool in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Deein

-
Reaction score
1
I have been trawling tge regs looking for clear rega concerning the proximity that a 3 phase mobile device can be installed in a swimmimg pool area.

A client wants a cooking unit installed that has 3x 3kw cooking appliances.
The 3 phase main switches are 32amp each as the incomming feeds are 10mm.
This prevents all 3 devices being installed on a single phase due to over amp demands.
I could run an armoured external to the area providing 3 phase, a phase to each device within the cooking unit.
However i cannot find clear definitions regarding this beung permittable.

The pool had no barrier, the unit is on wheels and client wants 15m flex to allow the device to be moved to diferent areas.
Seeing the pool is within 4m of requested outlet, any thing goes wrong the unit could end up in the middle of the pool.

I want to confirm i cannot do thia job, just want the regs to back up my decesion.

Any help you can offer lol
 
I have been trawling tge regs looking for clear rega concerning the proximity that a 3 phase mobile device can be installed in a swimmimg pool area.

A client wants a cooking unit installed that has 3x 3kw cooking appliances.
The 3 phase main switches are 32amp each as the incomming feeds are 10mm.
This prevents all 3 devices being installed on a single phase due to over amp demands.
I could run an armoured external to the area providing 3 phase, a phase to each device within the cooking unit.
However i cannot find clear definitions regarding this beung permittable.

The pool had no barrier, the unit is on wheels and client wants 15m flex to allow the device to be moved to diferent areas.
Seeing the pool is within 4m of requested outlet, any thing goes wrong the unit could end up in the middle of the pool.

I want to confirm i cannot do thia job, just want the regs to back up my decesion.

Any help you can offer lol
Well Mate you have BS7671 s you should know how to navigate your way through it.
 
Would have thought a risk assessment alone would preclude that being installed anywhere near a swimming pool. I would not install it. The only cooking I could see being done is the people in the pool. Recipe for disaster.
 
What you are describing I am having trouble making sense of. You seem to be saying three different cooking appliances at 3kw each yes? And they are OCPD device is 32a for what is circa 13a per device?
 
A client wants a cooking unit installed that has 3x 3kw cooking appliances.
The 3 phase main switches are 32amp each as the incomming feeds are 10mm.
This prevents all 3 devices being installed on a single phase due to over amp demands.
I could run an armoured external to the area providing 3 phase, a phase to each device within the cooking unit.
However i cannot find clear definitions regarding this beung permittable
it would not be advisable to put any appliance's near sources of water especially swimming pools unless it behind a glass wall .
 
The best you could do would be to install several sockets in the areas they want use of the cooker and fit a very short flex on the cooker.
 
One cooking trolly.
3 heat devices. Each just under 3kw.
2.6-2.9kw.

The 32amp is on each phase on incomming main protecting the 10mm frim main to consumer unit.



And yes...

I dont want to do the job.


Just want to quote regs to client so he understands and dont get someone shady to install.
 
Just want to quote regs to client so he understands and dont get someone shady to install.
Well get your copy of the regs out and find ones that back you up then, we aint a free design service on here without some input of what you have done first.
 
get the bloody thing installed and make sure you add a 4 way extension lead. darwinism will then come into play, but make sure you get paid.
Accident-Waiting.jpg


upload_2018-6-30_21-36-30.jpeg
 
https://electrical.------.org/media/1706/swimming-pools-no-need-to-make-waves.pdf

and see page 17 of 36 of

https://electrical.------.org/media/1055/2012_42_spring_wiring_matters__complete_adverts.pdf

and table at 2 of 4 of:

https://electrical.------.org/media...special-installations-or-locations-part-1.pdf

There should be some guidance in these (or later IET wiring matters pieces).

I googled 'IET wiring matters swimming' and 'IET wiring matters special locations'.
 
Last edited:
And here is Guidance Note 7 for special locations:

Guidance Note 7 - Special Locations - https://electrical.------.org/wiring-matters/issues/33/guidance-note-7-special-locations/
 

Reply to 3 phase regs in proximity to swimming pool in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
954
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
607
Hi Everyone! You all seem like a friendly bunch and google keeps referring me back to here but I still cannot find any solid answers so...
Replies
20
Views
3K
I have been asked to fit a 3 Phase 32 amp socket in a refrigerated area thats under construction. The cables will be on the walls and then a...
Replies
1
Views
764
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock