Discuss 3-Phase Supply Configuration, Mixed Commercial and Residential Installation in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
194
I have a potential customer, in Scotland, with mixed commercial and residential premises. The property was formerly a pub with a property of multiple occupancy upstairs. The property currently has a 3-phase TN-C-S supply coming in to the DNO's fused distribution box in the attic, second floor, which supplies 3 single phase meters. The attic does not have full standing height and other than housing the DNO's supply it will become a storage area!


The DNO's 100 A fuses are labelled on the face of the distribution box below them with a Red, Yellow and Blue spot. Live feeds are supplied from the top of the box: the 'Red' phase feeds a Wylex 7-way metal CU via a modern digital meter with onward connection to 2 metal CUs in the First Floor accommodation; the 'Yellow' phase is connected via the same type of digital meter to a Hager 4-way metal enclosure with a single double pole switch which is believed to be redundant. Neutral feeds are provided to these meters via a single neutral cable from the bottom of the distribution box to a 3-way Henley block providing a separate distributor's tail to each meter. Earth connections are provided to the active and redundant CUs in the same way. The 'Blue' phase distributor's live and neutral tails are supplied from the top of the box and are fed in parallel to the dual rate, 'Economy 7', meter and what appears to be a time clock below. The consumer's tails from this meter are further split at 2 Henley blocks to provide 2 live and 2 neutral tails. Up to this point, the installation is clean, neat and tidy. The exact nature and quality of the rest of the installation is, at this moment, an unknown quantity. It is believed that the CUs in the first floor accommodation are within 2 m of the supply point.


The customer requires a domestic installation in the residential part of the premises, a substantial 3-4 bedroomed flat with 3 large double bedrooms and a very large living room. The commercial premises requires a single phase supply for normal services and a 3-phase supply to a kitchen facility for the Cafe Bar.


Statement 1 - The current DNO's arrangement is unsuitable for the customer's requirement and they should contact the DNO to reconfigure the supply. Discuss.


What configuration should I expect? Will an additional single phase supply be required? I am thinking that there will need to be at least a single phase meter for the residential premises and a 3-phase meter for the commercial premises. Will the DNO require a separate single phase meter for the commercial premises? Will the single phase for the commercial premises be drawn from one of the 3 phases supplying the kitchen? Who will be responsible for delivering the connection to the customer's tails for the single phase supply to the commercial premises?


Statement 2 - The customer's desire for a 3-phase supply in order to capitalise upon the lower cost of second hand 3-phase electrical kitchen equipment is a false economy as the total through-life costs of design, installation, testing, maintenance and disposal of both the installation and the equipment are likely to be more expensive! Discuss.


The customer has plans drawn up by an architect, now sacked, who appears to have failed to correctly record the customer's requirements. It has taken 3 hours of consultation to discover and roughly record the customer's 'current' requirements; no other competitor has consulted in this manner with the customer and appear to have taken the drawings at face value. The customer wants: maximum reuse of existing fixtures, fittings and infrastructure; a list of parts to purchase and a labour only quotation.


Statement 3 - I should walk away as further effort is unlikely to bring just rewards! Discuss.


The customer clearly has a requirement ... even if some aspects of it are unachievable or misguided etc. In order for a win-win situation to prevail, would you insist that in order to provide a realistic parts list and estimate for labour that the customer pay for an up-front comprehensive electrical inspection and test which would enable the real scope of the work to be identified, agreed and costed? If I invest further effort in providing what the customer has asked for, how should I look to cover the investment of my time on the design and costing activity?
 
Might be worth asking customer to contact DNO for a TP meter and get rid of all the others , it may help with getting best prices for elec going fwd as well and must be easier to manage. If he goes for that then cable up TP and SP supplies as normal balancing where possible. I have to say though I have not asked for three Sp meters to be converted to one TP metered supply so am interested in what they say and how hard it is to make three separate supplies go to one.
 
How will changing the meter reduce the tariff? It’s not unusual to use summation metering via three separate meters. The readings of each meter are simply added together and put on one bill.

The first place I worked had 9 incoming meters (3 feeders), the last 15 (5 feeders). They only got one big bill.
 
Dan,

"The customer wants: maximum reuse of existing fixtures, fittings and infrastructure; a list of parts to purchase and a labour only quotation."

You ask an interesting question ... they are restoring OR renovating a Grade 'B' listed building on a shoe string budget; so I would say 'making the best of things'.
 

Reply to 3-Phase Supply Configuration, Mixed Commercial and Residential Installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
283
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
954

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock