Discuss 3 Phase Supply Voltage Problem (Russia) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi, my wife and I are over in Russia where we have an almost completed house. We have a 220V 3 phase supply. Recently we have experienced some electrical problems, mainly related to low power - dim lights, etc.

I measured the voltages we are receiving at our house, which are -

Phase 1 : 182V
Phase 2 : 183V
Phase 3 : 165V

I then went to our electrical companies local supply station (where our electrical meter is located). I measured the voltages on the electrical companies side of the box, these are the same ie -

Phase 1 : 182V
Phase 2 : 183V
Phase 3 : 165V

I am completely stuck! Anyone have any ideas what can be causing the low and unbalanced voltages?

Thanks
 
Hi, when i look up Russia 3 phase, it is stating 220V single phase and 380V 3 phase. When you measured the voltages, are you measuring between phases or are these readings between phase and neutral / earth ?
Between phase readings are stated like this Phase 1 - Phase 2 V, Phase 2 - Phase 3V and Phase 3 - Phase 1.
Readings to neutral or earth are stated like this Phase 1 - N, Phase 2 - N , Phase 3 to Neutral.

So if your readings are between Phase and Neutral , then yes that is a significant reduced voltage and if your equipment. In this country we would simply call the local supply company and report it.
Hope this helps
 
220 volts in Russia are derived from utilizing 2 phases, so you just see 220V at sockets etc, makes it somewhat difficult when testing (Live) and safe isolation, remember 2 phases equal DP fusing.
In some cases though, and I'm not that sure of how they do it the manage to bring Land N into a property, whenever I contacted the UPDK sort of Russian supply Authority, they became very cagey, as if it was a State Secret, so at times it cost me some cheap Voltage indicators from Finland to get any work done, and as I didn't speak Russian that well, I never did get much info, by the way this was back in the Cold War era, things may have changed somewhat.
 
Any appreciable N-E voltage -- (earth stake !)
to give a clue (phase 3 sagging as neutral lifts ? )
(heavy un-balanced load on phase 3- Turned off over xmas ?)
(if not so , sounds like a "local feature")
..Could be a local strategy to limit demand on
phase 3 if it has a weakness
-- All Speculation --
 
If he's getting 173V-ish on average L-N at the moment the corresponding voltage L-L would be 300V. So I don't think that supply is supposed to be 220V L-L, just a regular 3P+N 220/380V service. Even in the 90s that was all I saw there, albeit at large sites not domestic, although I'm sure you're right about the older 220V supplies having sometimes been L-L from 3-phase delta.

I think the voltage is low and unbalanced because it's broken. Maybe someone can be remunerated to fix it.
 
I think the voltage is low and unbalanced because it's broken. Maybe someone can be remunerated to fix it.

I measured the voltages on the electrical companies side of the box. If the problem is their side, they pay (in theory) if our side, then we pay. Is there any way I can check to make absolutely sure which side the problem is?
 
Re #13: Over a week:

a. With your Main Switch Off measure the phase voltages at the input to the meter, the output of the meter and at the input to your Main Switch at say 0800, 1200, 1600 and 2000.

b. Now turn on the Main Switch and load up your supply by the same amount (say 40-50A) each time and measure the same voltages as in a) at 0800, 1200, 1600 and 2000.

Plot these on some graph paper. If the spacings between the voltage readings at the suggested times remains constant over the week then there is no variation in the impedance of the supply up to your Main Switch input.

Consider the volt drop between the meter and Main Switch - is it reasonable for Russian wiring and the cable size between meter and Main Switch and constant between MS Off and MS On with load.

What do you observe for the phase voltages at the input and output of the meter? Any variation over a day or a week?

You may now have some evidence to show the fault lies beyond your property in the supply network. If it is a constant low supply voltage or a varying supply voltage is also useful to know. The former indicates something permanent - eg HV/LV transformer winding volt taps or a 24/7 large load sharing the same part of the LV network as you - whereas the latter could also include some poor connections or inadequate network cable sizes.
 
Last edited:

Reply to 3 Phase Supply Voltage Problem (Russia) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
358
Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Replies
1
Views
239
Hi I have UPS 50KVA and the inverter output AC voltage is feeding a distribution panel 120/208 V 4 wires when I check UPS display it shows me...
Replies
1
Views
280
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
306

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock