Search the forum,

Discuss 300 mA RCD main switch agricultural (tripping) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
30
Hi there thank-you for taking the time to read this! I have a 300mA Rcd in a grain shed on a farm now every time I try reset it won’t stay on there are 3 phases that go into the main switch
And it isolates all 3 bar the neutral so when wen everything is turned off mcb rcbo in the board it still trips iam guessing this is through the neutral if I could some how isolate the neutral and then hopefully it would stay up then turn one on at a time thoughts on fault finding ?
 
You'll need to disconnect each circuit and insulation resistance test them to identify which one(s) are causing the problem. I'd also test the RCD and you'll need to disconnect the outgoing neutral to be able to do this.
 
It will be an earth neutral fault OR if the testing of the RCD has been neglected, and the thing hasn't been off for years, it could be the mechanism sticking. Been working on farm electrics for 45 years, and have come across this on numerous occasions.
Testing needs to be done with an IR tester, operated by someone who knows how to use it.
 
Is this a main switch for the whole installation or a sub board? If you have a 3phase RCD it should have the neutral running through it too i.e. 4pole. If you have single phase loads then the rcd will see an inballence due to current flowing back through the neutrals.
Either that or you have a neutral earth fault as mentioned above.
Have you any pictures?
 
You'll need to disconnect each circuit and insulation resistance test them to identify which one(s) are causing the problem. I'd also test the RCD and you'll need to disconnect the outgoing neutral to be able to do this.
I would need to turn every switch off to insulation resistance test it so no lights etc get damaged this is the 2nd rcd main switch I have out in because thought it was faulty put the other one in and tripped straight away wouldnt let me out it on
 
It will be an earth neutral fault OR if the testing of the RCD has been neglected, and the thing hasn't been off for years, it could be the mechanism sticking. Been working on farm electrics for 45 years, and have come across this on numerous occasions.
Testing needs to be done with an IR tester, operated by someone who knows how to use it.
The cable feeding the new 3 phase board that a spark done then I took over was working fine then the grain dryer had a borrowed neutral that had to be disconnected now is there anychance he’s got his phases mixed up with it being an armour and the beautiful could be live
 
Is this a main switch for the whole installation or a sub board? If you have a 3phase RCD it should have the neutral running through it too i.e. 4pole. If you have single phase loads then the rcd will see an inballence due to current flowing back through the neutrals.
Either that or you have a neutral earth fault as mentioned above.
Have you any pictures?
Main switch is for the whole installation now I have sub boards off this running icleast 20 meters then 4 led strip lights also part of the old lights are wired to in armour nightmare
 
I would need to turn every switch off to insulation resistance test it so no lights etc get damaged this is the 2nd rcd main switch I have out in because thought it was faulty put the other one in and tripped straight away wouldnt let me out it on
You can test line and neutral together in one Croc clip to earth in the other Croc clip. This prevents any equipment from getting damaged.
 
Main switch is for the whole installation now I have sub boards off this running icleast 20 meters then 4 led strip lights also part of the old lights are wired to in armour nightmare
 

Attachments

  • image.jpg
    373.7 KB · Views: 9
  • image.jpg
    403.6 KB · Views: 10
Have you a picture of it installed?
If it was working and now is not what has changed since it last worked? It could be the weather or rodent damage.
Are the RCBO's single pole? Could still be a neutral earth fault on one of those if they are.
 
Have you a picture of it installed?
If it was working and now is not what has changed since it last worked? It could be the weather or rodent damage.
Are the RCBO's single pole? Could still be a neutral earth fault on one of those if they are.
I will get a pic on Friday mate what has changed is the old bud bar system he re routed the cable that fed that to a main switch then the grain dryer was a borrowed neutural then we left it on a normal main switch for time being and when we put it back in I tripped once grain dryer was removed
 

Reply to 300 mA RCD main switch agricultural (tripping) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
404
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
872
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
834
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top