Distribution unit 100A 300ma 3phase RCD with four 60A BS88 each fuse feeds 4 boxes on one circuit with 2X16 socket outlets with own individual 30ma RCBOs but there ok and all being plugged into
The RCD keeps tripping? Have tested the distribution unit and all the boxes with IR test and RCD I’ve the earth leakage with all loads connected and disconnected can’t see a problem but there saying it’s nuisance tripping at vary periods within a month for instance,
Can this be an imbalance on the phases?
Or overload of 100A??
 
an overload will not trip a RCD. have you tested the RCD? try a RCD test with circuits connected and then again with circuits dissed. also ramp test in both situations. if readings are different, then the problem is in the circuits. e.g. if a ramp test gives 275mA with no circuits connected, and 140mA with them connected, then you have somewhere around 135mA leakage on the circuits.
 
an overload will not trip a RCD. have you tested the RCD? try a RCD test with circuits connected and then again with circuits dissed. also ramp test in both situations. if readings are different, then the problem is in the circuits. e.g. if a ramp test gives 275mA with no circuits connected, and 140mA with them connected, then you have somewhere around 135mA leakage on the circuits.
Thanks will try that, what I mean is over current or inrush? I know the over current has protection with the 60A fuses
 
Is it an old wylex one? Ive had so many of them over the years trip randomly yet test out fine
Nope it’s not, they’ve had Board out to check there end as it’s over head supply and possibly thought it was a spike in voltage as it’s really random like could trip off for a few hours then be alright and then not trip for say a month but all cables IR tested all ok just gotta go back to ramp test
 
I’ve the earth leakage with all loads connected and disconnected can’t see a problem but there saying it’s nuisance tripping a
If I am reading this correctly what was the leakage with all the loads connected and disconnected? Also, have you done a ramp test on the 300mA RCD?
 

Reply to 300ma RCD tripping randomly in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
909
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
571
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
Replies
25
Views
6K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock