I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the night. TNC-S, rewired couple of years ago (not by me).

Three circuits on this RCCB: Cooker, Downstairs sockets, Downstairs lights (I know - dumb layout…)
  • all tested for insulation resistance to earth at 250V (all >99M), also tested ins res between these circuits, all >99M;
  • earth leakage clamp revealed 7mA on cooker, 7mA on ring, and 2mA on lights. This was steady state. When first switched on, earth leakage spiked higher.

Couldn’t find a smoking gun so I put this down to either cumulative fault current, or an intermittent fault on an appliance. I reconfigured the board so these 3 circuits were on separate RCBOs, in the hope that either it would cure the problem or at least narrow down the search.
All fine for a week or so.

Then - phone call - both the cooker and downstairs sockets RCBOs had tripped simultaneously. And the lady thought the downstairs lights flickered a second or two before.

Any thoughts? I don’t know where to go next with this. I went back today and rechecked the insulation resistance and clamped for fault current - no change to the above.

It tripped again the same way this evening and this time they were 100% sure the lights went dim immediately before.

There’s no leakage between these circuits so how can two RCBOs be tripping simultaneously, and what is causing the lights to dim???
 

Attachments

  • BCD7A293-5555-4CCE-8E8A-0B1B51B8B0E4.jpeg
    323.4 KB · Views: 30
If I were to guess id say there is a low resitance between both L&N to earth on one of the circuits.. quite often the circuit effected wont trip as the imbalance is shared (both L&N) so the coil on the rcd wont trip.. it can creep ect other unrelated RCDs. Though



































































































































































































Whats going on with the forum having real trouble replying it's adding loads of spaces
 
Last edited:
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the night. TNC-S, rewired couple of years ago (not by me).

Three circuits on this RCCB: Cooker, Downstairs sockets, Downstairs lights (I know - dumb layout…)
  • all tested for insulation resistance to earth at 250V (all >99M), also tested ins res between these circuits, all >99M;
  • earth leakage clamp revealed 7mA on cooker, 7mA on ring, and 2mA on lights. This was steady state. When first switched on, earth leakage spiked higher.

Couldn’t find a smoking gun so I put this down to either cumulative fault current, or an intermittent fault on an appliance. I reconfigured the board so these 3 circuits were on separate RCBOs, in the hope that either it would cure the problem or at least narrow down the search.
All fine for a week or so.

Then - phone call - both the cooker and downstairs sockets RCBOs had tripped simultaneously. And the lady thought the downstairs lights flickered a second or two before.

Any thoughts? I don’t know where to go next with this. I went back today and rechecked the insulation resistance and clamped for fault current - no change to the above.

It tripped again the same way this evening and this time they were 100% sure the lights went dim immediately before.

There’s no leakage between these circuits so how can two RCBOs be tripping simultaneously, and what is causing the lights to dim???
make sure the neutrals are on the right rcds the other cause could be mice eating the cable which might account for the lights going dim
 
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the night. TNC-S, rewired couple of years ago (not by me).

Three circuits on this RCCB: Cooker, Downstairs sockets, Downstairs lights (I know - dumb layout…)
  • all tested for insulation resistance to earth at 250V (all >99M), also tested ins res between these circuits, all >99M;
  • earth leakage clamp revealed 7mA on cooker, 7mA on ring, and 2mA on lights. This was steady state. When first switched on, earth leakage spiked higher.

Couldn’t find a smoking gun so I put this down to either cumulative fault current, or an intermittent fault on an appliance. I reconfigured the board so these 3 circuits were on separate RCBOs, in the hope that either it would cure the problem or at least narrow down the search.
All fine for a week or so.

Then - phone call - both the cooker and downstairs sockets RCBOs had tripped simultaneously. And the lady thought the downstairs lights flickered a second or two before.

Any thoughts? I don’t know where to go next with this. I went back today and rechecked the insulation resistance and clamped for fault current - no change to the above.

It tripped again the same way this evening and this time they were 100% sure the lights went dim immediately before.

There’s no leakage between these circuits so how can two RCBOs be tripping simultaneously, and what is causing the lights to dim???
That makes sense but wouldn’t that show when testing insulation resistance between these circuits? I get >99MOhms L-L, L-N, N-L, N-N
Have you checked for crossed over neutrals?
Or one I had some years ago where there was an unterminated cable waaaay up high for an outside light that caused intermittent rcd issues, only tripped when it reined from a certain direction caused the end of the cable to get damp. took ages to trace
 
If it worked before, then it’s a new fault developed. Wrongly connected would show up straight away.

anything new been added to any of the circuits?

Smart meter? Long shot, but it’s happened before.

Individually, we might think an outside light or socket taking in water, or rodent damage… but for all 3 at same time?
What is the likelihood of rodents? Near fields?
 
If it worked before, then it’s a new fault developed. Wrongly connected would show up straight away.

anything new been added to any of the circuits?

Smart meter? Long shot, but it’s happened before.

Individually, we might think an outside light or socket taking in water, or rodent damage… but for all 3 at same time?
What is the likelihood of rodents? Near fields?
Rodents - Very unlikely. Urban property. Kept immaculate. Recently gutted and refurbed (2 hrs ago ish)
 
Have you checked for crossed over neutrals?
Or one I had some years ago where there was an unterminated cable waaaay up high for an outside light that caused intermittent rcd issues, only tripped when it reined from a certain direction caused the end of the cable to get damp. took ages to trace
Checked for crossed neutrals, it’s not that. Can’t rule out an unterminated cable somewhere but the tripping doesn’t link with rain. And that would only take out the one RCBO.
 
If the circuits are completely separated as you claim, yet both trip simultaneously then there has to be a common factor that you have not inspected. If the lights do indeed dim just before the RCBO's trip then this may point to an intermittent imbalance mains issue. Have you checked the incomer and associated connections?
 
If it worked before, then it’s a new fault developed. Wrongly connected would show up straight away.

anything new been added to any of the circuits?

Smart meter? Long shot, but it’s happened before.

Individually, we might think an outside light or socket taking in water, or rodent damage… but for all 3 at same time?
What is the likelihood of rodents? Near fields?
house mice don't need fields lol
 
If the circuits are completely separated as you claim, yet both trip simultaneously then there has to be a common factor that you have not inspected. If the lights do indeed dim just before the RCBO's trip then this may point to an intermittent imbalance mains issue. Have you checked the incomer and associated connections?
I think you’re onto something there – I got the customer to ask around in the street last night, and one of his neighbours two doors down had exactly the same issue at exactly the same time, so I am thinking there is a problem with the supply in The Street. I’ve got him to raise the issue with the DNO. The only bit I have not checked is the switch fuse and sub main from my customers meter to his CU.
 
All fine for a week or so.
This is possibly the biggest clue.
As well as pursuing investigating a supply issue....

I'd be thinking whether anything might be out of circuit when testing that is in circuit during the fault.
Do they have any outside lights or anything time clock controlled?
e.g. an outside light switched by a double pole switch on the ring that is also linked to a PIR fed by the lighting circuit with all neutrals joined up, or something similarly special.

I'd also take a look at the boiler wiring if it's on the downstairs sockets circuit as when combi's are fitted all sorts of delightful things are done by our friends who fit them.

Have you tested the cooker itself? A cooker with a slowly developing N-E fault touching a bonded gas pipe behind can be the source of interesting fault chasing as the thing triggering it can be anything that is earthed.

I'd also try to be thinking about whether there is anywhere that the circuits run together. I remember one very obscure fault where cables had been pulled hard and they'd cut into some metal trunking, and vibrations changed the IR from absolutely fine to practically zero.

Best of luck and do report back!
 

Reply to Two RCBOs tripping together, no cross-connection. Need help… in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
996
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
834
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
791
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock