I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the night. TNC-S, rewired couple of years ago (not by me).

Three circuits on this RCCB: Cooker, Downstairs sockets, Downstairs lights (I know - dumb layout…)
  • all tested for insulation resistance to earth at 250V (all >99M), also tested ins res between these circuits, all >99M;
  • earth leakage clamp revealed 7mA on cooker, 7mA on ring, and 2mA on lights. This was steady state. When first switched on, earth leakage spiked higher.

Couldn’t find a smoking gun so I put this down to either cumulative fault current, or an intermittent fault on an appliance. I reconfigured the board so these 3 circuits were on separate RCBOs, in the hope that either it would cure the problem or at least narrow down the search.
All fine for a week or so.

Then - phone call - both the cooker and downstairs sockets RCBOs had tripped simultaneously. And the lady thought the downstairs lights flickered a second or two before.

Any thoughts? I don’t know where to go next with this. I went back today and rechecked the insulation resistance and clamped for fault current - no change to the above.

It tripped again the same way this evening and this time they were 100% sure the lights went dim immediately before.

There’s no leakage between these circuits so how can two RCBOs be tripping simultaneously, and what is causing the lights to dim???
 

Attachments

  • BCD7A293-5555-4CCE-8E8A-0B1B51B8B0E4.jpeg
    323.4 KB · Views: 36
If I were to guess id say there is a low resitance between both L&N to earth on one of the circuits.. quite often the circuit effected wont trip as the imbalance is shared (both L&N) so the coil on the rcd wont trip.. it can creep ect other unrelated RCDs. Though



































































































































































































Whats going on with the forum having real trouble replying it's adding loads of spaces
 
Last edited:
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the night. TNC-S, rewired couple of years ago (not by me).

Three circuits on this RCCB: Cooker, Downstairs sockets, Downstairs lights (I know - dumb layout…)
  • all tested for insulation resistance to earth at 250V (all >99M), also tested ins res between these circuits, all >99M;
  • earth leakage clamp revealed 7mA on cooker, 7mA on ring, and 2mA on lights. This was steady state. When first switched on, earth leakage spiked higher.

Couldn’t find a smoking gun so I put this down to either cumulative fault current, or an intermittent fault on an appliance. I reconfigured the board so these 3 circuits were on separate RCBOs, in the hope that either it would cure the problem or at least narrow down the search.
All fine for a week or so.

Then - phone call - both the cooker and downstairs sockets RCBOs had tripped simultaneously. And the lady thought the downstairs lights flickered a second or two before.

Any thoughts? I don’t know where to go next with this. I went back today and rechecked the insulation resistance and clamped for fault current - no change to the above.

It tripped again the same way this evening and this time they were 100% sure the lights went dim immediately before.

There’s no leakage between these circuits so how can two RCBOs be tripping simultaneously, and what is causing the lights to dim???
make sure the neutrals are on the right rcds the other cause could be mice eating the cable which might account for the lights going dim
 
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the night. TNC-S, rewired couple of years ago (not by me).

Three circuits on this RCCB: Cooker, Downstairs sockets, Downstairs lights (I know - dumb layout…)
  • all tested for insulation resistance to earth at 250V (all >99M), also tested ins res between these circuits, all >99M;
  • earth leakage clamp revealed 7mA on cooker, 7mA on ring, and 2mA on lights. This was steady state. When first switched on, earth leakage spiked higher.

Couldn’t find a smoking gun so I put this down to either cumulative fault current, or an intermittent fault on an appliance. I reconfigured the board so these 3 circuits were on separate RCBOs, in the hope that either it would cure the problem or at least narrow down the search.
All fine for a week or so.

Then - phone call - both the cooker and downstairs sockets RCBOs had tripped simultaneously. And the lady thought the downstairs lights flickered a second or two before.

Any thoughts? I don’t know where to go next with this. I went back today and rechecked the insulation resistance and clamped for fault current - no change to the above.

It tripped again the same way this evening and this time they were 100% sure the lights went dim immediately before.

There’s no leakage between these circuits so how can two RCBOs be tripping simultaneously, and what is causing the lights to dim???
That makes sense but wouldn’t that show when testing insulation resistance between these circuits? I get >99MOhms L-L, L-N, N-L, N-N
Have you checked for crossed over neutrals?
Or one I had some years ago where there was an unterminated cable waaaay up high for an outside light that caused intermittent rcd issues, only tripped when it reined from a certain direction caused the end of the cable to get damp. took ages to trace
 
If it worked before, then it’s a new fault developed. Wrongly connected would show up straight away.

anything new been added to any of the circuits?

Smart meter? Long shot, but it’s happened before.

Individually, we might think an outside light or socket taking in water, or rodent damage… but for all 3 at same time?
What is the likelihood of rodents? Near fields?
 

Reply to Two RCBOs tripping together, no cross-connection. Need help… in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
755
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
852
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock