Discuss 32A Wago clips for an electrical socket spur? in the Electrical Tools and Products area at ElectriciansForums.net

Reaction score
2
Hi!

I've got a couple of 32A Wago clips. Creating a spur socket from a ring circuit with these is quite easy, but I wanted to know if it's advised from a safety standpoint?

When wiring an electrical socket, having these as opposed to having multiple cables going into the holes in the socket?

Would this also work in spurs within radial circuits?

thanks!
 
their is no advantage in using them for a spur from a ring, the socket terminals are designed to take 3 x 2.5mm cables and often more than that.
adding extra joints in any electrical system is bad practice (in my opinion) when they are not required.
 
Always use the 32A+ ones on 32A ring circuits, if there is a fault in the ring then both 'halves' of the ring are attached to a 32A supply. The little 20A max push-fit ones are great for lighting but I wouldn't use them on a ring.

Have you seen the double sockets with wago's on the back? They look awesome in the wholesalers until you see the price difference, they all have triple wago's on designed for spurring
 
apart from anything else, its the approximate rating of 2.5mm cable enclosed in conduit or a wall.
also, often the rating of a terminal on a standard socket.
 

Reply to 32A Wago clips for an electrical socket spur? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
746
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
757
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
295

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock