Search the forum,

Discuss 3Kw Immersion Heater circuit using trunking in the Australia area at ElectriciansForums.net

O

olsonn

Made the fatal mistake of offering to do a friend a favour which always comes back to bite you. Its a one bedroom flat with concrete floor and ceiling and only one ring final circuit for sockets. Wants panel heaters fitting in the hall 1.25Kw and bathroom 0.75 kw so i said i would run a new circuit to accomodate this using 2.5mm T&E in surface mounting mini trunking. At the same time I was also going to put in another circuit to take the 3Kw immersion heater which currently resides on the socket circuit. I had hoped to run this circuit in the same trunking as the other new circuit using 2.5mm T&E as it is such a bugger to drill through the concrete ceiling but having done a few calculations it looks like if I use the same trunking I would have to up the cable size to at least 4mm (the run is about 12m). Is this correct? Another sparky seems to think that there is a reg which says that cable for an immersion heater has to be in trunking by itself, but I couldn't find this anywhere in the regs
 
The space heating and immersion heater need to be on separate final circuits as you propose but the cables can be run in the same trunking, your sparky mate is wrong.
The two cables in the same trunking, installation methods 8&9 (reference method B), have a de-rating factor of 0.8 for the cable grouping. 2.5mm[SUP]2[/SUP] T&E would still be rated at 18.4A (Table 4D2A, 23Ax0.8) assuming you do not have any other de-rating factors, so would appear to be suitable for both final circuits.
 
Last edited by a moderator:
Thanks Markie that will solve the trunking problem, just need to check now if I need to up the cable size for the immersion final circuit
 
i would use table 4D5 for T/E flat cable which would give 20A x 0.8 =16A so would still be OK for the immersion.
 

Reply to 3Kw Immersion Heater circuit using trunking in the Australia area at ElectriciansForums.net

Similar Threads

I've purchased a horizontal unvented cylinder that has come with 2 immersion heaters. I was hoping to use the same circuit the my existing tank...
Replies
16
Views
2K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
708
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
225
Have a 63A RCD 5 Way box, with a 45A MCB, feds by 16mm2 tails, this in then feeding into a isolator via 10mm2 T&E, that then supplies the feed to...
Replies
8
Views
489
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock