Discuss 3P continuity L1 Earth in the UK Electrical Forum area at ElectriciansForums.net

Quick question for someone... Recently came across 3phase industrial heater, changing over a faulty isolator, in terminal box where equipment cable meets supply... I have continuity between L1 and Earth but nothing between L2 and L3 and earth. Disconnected earth from source and still the same.

View attachment 48072
Not good to have continuity between any Phases and Earth I would have thought, although your post is somewhat confusing.
 
So you have a possible short between L1 and earth??

Yeah so it's telling me, I have not checked to see if there is voltage there when powered up but I would think there would be if cont L1 E? Think ill need to look in heater panel, I have not replaced anything else so I am guessing its been running like that before
 
If you have a short from line to earth with a sufficiently low resistance it will trip the protective device, hopefully.
 
The heater probably has 3 elements.
L1 - N, L2 - N, L3 - N.
L1 element has probably burnt out and is now shorting L1 to E.


Sounds good to me mate ill indulge into that, prior to faulty isolator it was not going through cycle to start up, I was gonna look at air pressure stat but ill check this first, thanks
 

Reply to 3P continuity L1 Earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Reasonably competant non electrical engineer homeowner here. I have a question for the experts: I recently replaced a horrible...
Replies
8
Views
1K
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
746
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock