Hi guys,

I have a basic wiring test on Friday and I've been told one of the practical parts is wiring a 3ph heating element.

Does anyone have a basic diagram of how this should be done ??

TIA
 
Heres what it says.......

1) The candidate will connect a range of heating elements to a supply using industry best practice. The task will require the candidate to have a theoretical knowledge of three phase and good standards of workmanship. The task aims to establish if the candidate understands three phase wiring and wiring best practice.
 
first you need to know the voltage required by each element. if it's 230V, you connect them in star configuration. if it's 400V then you would connect as delta.
 
220px-The_basic_3-phase_configurations.svg.png
 
As this is for a test i'm assuming you have had coursework relevant to the subject so look through your coursework and express how you think it all should be done then we can tidy up the edges ...... asking on here without trying to give any solutions yourself will not aid you in your learning.... it may get you a pass but in the real world not knowing such things can be costly if not dangerous. So how do YOU! think you should do this now you have already been given help.... as your Q expresses 3ph we will assume 400v.
 
Very good point mate,

My main worry is how I wire between the element connections and the phases in delta.

If I say the connections at each element are.....
R1-R2 (first element)
R3-R4 (second element)
R5-R6 (third element)

L1---R1
R2---R3
L2---R4
R4---R5
L3---R6

Not had any dealings with 3ph since college and 8yr ago so don't laugh lol
 
A wrong phase connection & missing another connection!

Hint...Draw the 3 phases (elements) as a triangle :)

2nd edit...the answer is already on the thread (courtesy of Tel!)
 
This can get confusing quickly for newbies.... if it a duel voltage set-up then its the reverse of your post... Star 400v - Delta -230v that's why I asked for his draft on an answer to see what he's been taught, although i assume with his suggestion of 3ph we could rule out 230v.

what i meant was that assuming a 400V 3∅ supply, if each element required 230V then star. if each element required 400V (rare, i know) then delta.
 
I didn't read the whole thread yet but I think I'm at least as confused as the OP.
Ill edit it out probably not what he's been taught but i have used such element kits designed for European and American markets they connect delta we connect star. Like a duel voltage motor set-up.
 
Ahh, I'm with you now, it's not a very common set up

what i meant was that assuming a 400V 3∅ supply, if each element required 230V then star. if each element required 400V (rare, i know) then delta.
This is how I understood it.
 

Reply to 3ph Heating Element in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a princess 1500w smart glass panel heater which only chucks out half the heat it should. I've checked the thermal fuse with a...
Replies
2
Views
744
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
554
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock