Search the forum,

Discuss 4.5kw on 30a cooker in the UK Electrical Forum area at ElectriciansForums.net

What is your specific question? If it's 'How is diversity applied to a domestic cooker rating?" then no, it's not right.
 
OP - for next time when the appliance is bigger I've set out the diversity calculation for a 4.5 Kw cooker below. It's certainly the most confusing one.
Full load current: (4500/230)= 19.57amps
Set aside the first 10 amps, and work out 30% of remainder
9.57 amps x 0.3 = 2.81 amps
Add the first 10A back = 12.81 amps if no socket on switch
If there's a socket on the plate add 5 amps. 17.81 amps if it has socket

So when adding up maximum demand of the house you'd use the appropriate value.
 
16210867733263924940809269567237.jpg
was just reading this ..
 
For a long time I didn't have the on site guide. I finally relented a year or two ago and I'm still not sure it's worth the money. I favour the ProCerts apps for most things, and the OSG omits some useful tables for current carrying capacity of some cable types.
That page @i=p/u posted, and the couple before it are probably the only pages I use in it most of the time.
 

Reply to 4.5kw on 30a cooker in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock