Discuss 4.5kw on 30a cooker in the UK Electrical Forum area at ElectriciansForums.net

What is your specific question? If it's 'How is diversity applied to a domestic cooker rating?" then no, it's not right.
 
OP - for next time when the appliance is bigger I've set out the diversity calculation for a 4.5 Kw cooker below. It's certainly the most confusing one.
Full load current: (4500/230)= 19.57amps
Set aside the first 10 amps, and work out 30% of remainder
9.57 amps x 0.3 = 2.81 amps
Add the first 10A back = 12.81 amps if no socket on switch
If there's a socket on the plate add 5 amps. 17.81 amps if it has socket

So when adding up maximum demand of the house you'd use the appropriate value.
 
16210867733263924940809269567237.jpg
was just reading this ..
 
For a long time I didn't have the on site guide. I finally relented a year or two ago and I'm still not sure it's worth the money. I favour the ProCerts apps for most things, and the OSG omits some useful tables for current carrying capacity of some cable types.
That page @i=p/u posted, and the couple before it are probably the only pages I use in it most of the time.
 

Reply to 4.5kw on 30a cooker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
938
I have a L21-30 receptacle. Theoretically speaking, if I want to power a 30A load that requires a L5-30 receptacle, can I just use a L21-30 to...
Replies
2
Views
699
Bit of a strange one ive been told by everyone ive called had a triton t70xr 8.5kw The water started running cold like the tco kicked in after a...
Replies
3
Views
1K
Just wondering what everyone’s view on this is, if you’re mourning cooker or hob switch in cupboard close by. Would you still terminate into an...
Replies
7
Views
631
Hi, can someone please advise on where if anywhere I may acquire an adapter to duct out this old Elica cooker hood. The hole is 150mm x 90mm and I...
Replies
4
Views
382

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock