Discuss Are cooker outlets necessary!? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
73
Just wondering what everyone’s view on this is, if you’re mourning cooker or hob switch in cupboard close by. Would you still terminate into an outlet then go from there to cooker or hob? Or would you take the cable straight into the appliance
 
Some 45A DP switches have a built in flex clamp so this permits flexing directly to the isolating switch but it depends on location as not always close or convenient enough to flex directly to the isolator.
 
The point of an isolator is to provide isolation for maintenance, cleaning or in case of fire.
By my understanding of the regs it should be ;
1 Accessible
2 Labeled if the purpose is not obvious
3 If it is not a domestic installation it should be lockable.

It is understandable that customers may not want to have an isolator that is visible in their kitchen so instead of trying to hide them in cupboards why not put them beside the main board with a label on them?
Or am I wrong?
 
The point of an isolator is to provide isolation for maintenance, cleaning or in case of fire.
By my understanding of the regs it should be ;
1 Accessible
2 Labeled if the purpose is not obvious
3 If it is not a domestic installation it should be lockable.

It is understandable that customers may not want to have an isolator that is visible in their kitchen so instead of trying to hide them in cupboards why not put them beside the main board with a label on them?
Or am I wrong?
Yes. But nothing to do with the OP question!
 

Reply to Are cooker outlets necessary!? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
893
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
794
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock