Discuss 4.5kw water heater On 13A spur. in the UK Electrical Forum area at ElectriciansForums.net

Zdb

-
Esteemed
Reaction score
496
Got a 4.5kw water heater that comes with a 1.5mm2 flex from the manufacturer that looks like its meant to be wired into a 20A DO switch. My question is, isn't the size borderline as 4.5kw = 19+ amps?

Thanks

Edited from 13A
 
Last edited:
I meant 20A as in DP switch. So the 1.5mm is fine? I thought if the manufacturer supplied it it must be ok but thought I would double check on here.
 
IMG_2687.PNG
That is ridiculous and extremely silly from a 'professional' - obviously the nail would have to be 1" or it wouldn't fit !! :rolleyes:
I've got a good selection of fuse sizes that may meet your requirements
 
Most appliances still have their power ratings quoted at 240V not 230V, if this is the case here it will be 18.75A which is fine for a 20A supply. The power at 230V will be less.
 

Reply to 4.5kw water heater On 13A spur. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
232
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
905
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
431

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock