Discuss 45A breaker max Zs values in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

paj

-
Reaction score
0
Hi all,
Why is there no max Zs value for a 45A type B breaker in table 41.3 of 18th edition? What value should be used as max value on schedule of test results?
Cheers.
 
I got 0.93 using 225/230x95%
 
In addition to C min (0.95) to take account of voltage variation, do you have to incorporate a factor of 0.8 for temperature effects?

I.e. 230*0.95/ 5*45=218.5/225 =0.97

But to account for temperature effects the corrected value of Zs is 0.97*0.8 =0.77 ohms.
 
In addition to C min (0.95) to take account of voltage variation, do you have to incorporate a factor of 0.8 for temperature effects?

I.e. 230*0.95/ 5*45=218.5/225 =0.97

But to account for temperature effects the corrected value of Zs is 0.97*0.8 =0.77 ohms.

Yes. As a rule of thumb. More accurate compensations for temperature differences can be seen in Guidance Note 3, though this is rarely needed unless your design is getting close to limits.

The OP asked why 45A wasn't shown in the BBB, and these are the uncorrected values that everyone has supplied.

On certs I tend to state the corrected value for max Zs and put a footnote to say what I've done. To me this makes sense because further along you have your actual measured Zs and hence you get a quick cross check that your circuit complies. The question of whether to put corrected or uncorrected Maz Zs on Schedules of Inspections has been asked before and created some debate.....
 
On certs I tend to state the corrected value for max Zs and put a footnote to say what I've done. To me this makes sense because further along you have your actual measured Zs and hence you get a quick cross check that your circuit complies. The question of whether to put corrected or uncorrected Maz Zs on Schedules of Inspections has been asked before and created some debate.....[/QUOTE]

Thank you Marcus. It does make sense.
As a supplementary question:when calculating voltage drop do you always use the factor of 1.2 to account for temperature effects?
 
Thank you all for your prompt and useful replies.
I accept the point made by Rob about they can't include every device but I was surprised one as common as 45A wasn't there.
I understand that Cmin was introduced to allow a "safety factor" to the BS 7671 Zsmax values in consideration of possible supply voltage fluctuation i.e. the minimum voltage available may be as low as 95% of nominal (218.5V) under certain conditions.
We then use this min possible voltage divided by the operating current of the device, in this case 225A, to find the Zsmax which will ensure the device operates in the required disconnection time, even if the supply voltage is at its minimum. As per Marcus and Ian.
Moving onto the second bit of my query. This would be the "BS 7671 Zsmax value" to write in column 8 of the Schedule of Test Results if we follow the apparent meaning/spirit of the Regs? This value would still be subject to the 0.8 rule of thumb when comparing with measured test values. The footnote on the bottom of the schedule allows for values from other sources to be used if this is stated in column 25. An example could be taking an already corrected value from the OSG which still has the 45A Zs value listed.
I am not trying to be pedantic here but I am trying get to a correct firm procedure on how to deal with such issues. What is acceptable or not. I would agree totally with the logic of Marcus and Elecnewt, but it doesn't seem to fit with the intentions of the Regs. I am also thinking about lessening the confusion for those training in inspection and testing.

Thanks to all.
 
Thank you all for your prompt and useful replies.
I accept the point made by Rob about they can't include every device but I was surprised one as common as 45A wasn't there.
I understand that Cmin was introduced to allow a "safety factor" to the BS 7671 Zsmax values in consideration of possible supply voltage fluctuation i.e. the minimum voltage available may be as low as 95% of nominal (218.5V) under certain conditions.
We then use this min possible voltage divided by the operating current of the device, in this case 225A, to find the Zsmax which will ensure the device operates in the required disconnection time, even if the supply voltage is at its minimum. As per Marcus and Ian.
Moving onto the second bit of my query. This would be the "BS 7671 Zsmax value" to write in column 8 of the Schedule of Test Results if we follow the apparent meaning/spirit of the Regs? This value would still be subject to the 0.8 rule of thumb when comparing with measured test values. The footnote on the bottom of the schedule allows for values from other sources to be used if this is stated in column 25. An example could be taking an already corrected value from the OSG which still has the 45A Zs value listed.
I am not trying to be pedantic here but I am trying get to a correct firm procedure on how to deal with such issues. What is acceptable or not. I would agree totally with the logic of Marcus and Elecnewt, but it doesn't seem to fit with the intentions of the Regs. I am also thinking about lessening the confusion for those training in inspection and testing.

Thanks to all.
Other sources of values can come from the actual manufacturer of the ocpd rather than using the generic values given for common devices listed in chapter 41 of BS7671
 

Reply to 45A breaker max Zs values in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason! Anyway, Table I1 in the OSG says the mΩ/m value for...
Replies
2
Views
723
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
hello , can anyone reccomend a free download for max zs values for bs 3871 ct breakers please
Replies
2
Views
1K
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
1K
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
760

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock