Currently reading:
4mm radials

Discuss 4mm radials in the UK Electrical Forum area at ElectriciansForums.net

JonathanA

DIY
Reaction score
1
Morning all,

I‘d really appreciate some advice - not a kick in the pants please - from those more knowledgeable than me!

My new kitchen and utility room are each supplied by 4mm T&E radials. Each circuit is protected by a 32A RCBO.

Kitchen
  • Single oven rated at 2.5kW connected to single socket at end of radial
  • Toaster, kettle, fridge and microwave connected to 3 x double sockets leaving some spare

Utility
  • Washing machine connected to single socket
  • Vented dryer connected to single socket
  • Boiler connected to 3A fused switch
  • 2 x double sockets spare

Length of radial in both cases is less than 10m so no worries there.

I was told that a 4mm radial with 32A protection is a ’standard circuit’ but there are issues with the installation that bother me, specifically:

1) The oven is not on a separate circuit so it’s not a ‘standard circuit‘ at least according to the OSG
2) The cabling for the most part is clipped direct but it is boxed in with other loose cables for a run of about 2m.
3) All the cables from the consumer unit descend loosely through a void in an otherwise insulated stud wall before going their separate ways (I suspect my OCD is kicking in with this one)

My worry of course is the possibility of the 4mm cables becoming overloaded at less than 32A.

Please understand that rewiring either of these circuits or installing new ones would involve huge disturbance which I am very keen to avoid.

I would sleep easier if the RCBOs were down rated to 25A but Wylex only make compact types for this rating which wouldn’t match the others in the CU.

I’d really appreciate your advice on this. Best response would be to tell me it’s fine, that I’m overthinking it and should get a life!

Thanks, J
 
I'd rather have a open L or N leg on a ring than an open Earth leg on a radial.
I’d rather not have any open legs on either.
That’s where regular testing comes in ?

rule of thumb, 4A per kW... so your 2.5kW oven takes 10A.... kettle? Maybe the same. Fridges, hood extractor etc are very little in comparison.
 
Morning all,

I‘d really appreciate some advice - not a kick in the pants please - from those more knowledgeable than me!

My new kitchen and utility room are each supplied by 4mm T&E radials. Each circuit is protected by a 32A RCBO.

Kitchen
  • Single oven rated at 2.5kW connected to single socket at end of radial
  • Toaster, kettle, fridge and microwave connected to 3 x double sockets leaving some spare

Utility
  • Washing machine connected to single socket
  • Vented dryer connected to single socket
  • Boiler connected to 3A fused switch
  • 2 x double sockets spare

Length of radial in both cases is less than 10m so no worries there.

I was told that a 4mm radial with 32A protection is a ’standard circuit’ but there are issues with the installation that bother me, specifically:

1) The oven is not on a separate circuit so it’s not a ‘standard circuit‘ at least according to the OSG
2) The cabling for the most part is clipped direct but it is boxed in with other loose cables for a run of about 2m.
3) All the cables from the consumer unit descend loosely through a void in an otherwise insulated stud wall before going their separate ways (I suspect my OCD is kicking in with this one)

My worry of course is the possibility of the 4mm cables becoming overloaded at less than 32A.

Please understand that rewiring either of these circuits or installing new ones would involve huge disturbance which I am very keen to avoid.

I would sleep easier if the RCBOs were down rated to 25A but Wylex only make compact types for this rating which wouldn’t match the others in the CU.

I’d really appreciate your advice on this. Best response would be to tell me it’s fine, that I’m overthinking it and should get a life!

Thanks, J
From the way you have described the installation methods, the only thing I would watch out for is the 'grouping' Cg factor and that the circuits are spaced from each other in that void. Even still there is an element of diversity for the expected loads on these circuits. Personally I believe you are 'over-thinking' this! But without see the installation these are merely assumptions.
 

Attachments

  • Report Export.pdf
    372 KB · Views: 12

Reply to 4mm radials in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top