Hi, just finished a partial rewire at my sisters house and when testing the two lighting circuits (up&down) the 6AMCB trips for both circuits individually, I thought the MCBs might just be sensitive to the test but the smoke alarm circuit also 6A is fine when testing, R1+R2 and IR test all fine just the Loop test causing issues, any ideas??

Thanks Lewis
 
Answer to all three above, the circuits have rcd protection, was a three prob test, megger 1552 tester and that is what I did in the end add r1+r2 to Ze just the fact it tripped two off the 6a mcbs and not all three is what threw me off.
 
Hi - Do I understand correctly (?) you are trying to measure Zs on a circuit using the low current test (due to RCD presence) and the OCPD trips.
 

Reply to 6A MCB Tripping on Earth Fault Loop Impedance Test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
875
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all Just a quick one. For a fire alarm loop addressable system. Fp200 1.5mm cpc 1.5mm To obtain R1+R2 would you treat the "loop" as a...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock