Hi Guys,
I have started a PIR at a house today and the cooker supply leaves the CU as a 6mm T+E (32amp MCB) and at the cooker Switch it's a 2.5mm T+E.

The previous owner was a real cowboy. :(

I'm guessing the old cooker switch was in the wrong place so he extended it with 2.5 T+E and sealed the joint in the wall.

The cooker is a fan oven the kind that comes with a 13amp moulded plug.
I know I want them to rip the kitchen apart, but I don't think it is in there budget, so what do you think about down grading the circuit to a 15amp radial.

any thoughts?
 
A PIR is exactly that.

You only need to report of the condition of the installation and not rectify anything, unless they have asked you to.

If so, i would downgrade to 20A MCB and note it on the PIR.
 
A PIR is exactly that.

You only need to report of the condition of the installation and not rectify anything, unless they have asked you to.

The customer is having lighting problems (re cowboy previous owner) mainly cheap transformers but there is a wall light that I can't find a connection to any circuit. so there are other issues

If so, i would downgrade to 20A MCB and note it on the PIR.

Thanks it is at present a 32amp cartridge fuse, but the customer wants a CU upgrade so I will not it on the PIR and downgrade to a 15amp MCB

Richard
 
First question. What is the cooker loading? Many moden cookers have electric ovens and gas hobs, in which case the load is likely to be in the order of 10Amps. Is there a 13A outlet

2.5mm T&E is normally rated 20A so you coulld use a 20A MCB, (ie unless there is stud around).

If there is an electric hob then start stripping the kitchen.
 
First question. What is the cooker loading? Many moden cookers have electric ovens and gas hobs, in which case the load is likely to be in the order of 10Amps. Is there a 13A outlet

2.5mm T&E is normally rated 20A so you coulld use a 20A MCB, (ie unless there is stud around).

If there is an electric hob then start stripping the kitchen.


No it is a gas (seperate) hob and a seperate fan oven.

I was just double checking what I thoiught.

Thanks for your help everyone :)
 

Reply to 6mm T+E becomes 2.5 T+E at cooker point in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
905
Is this ok? 32amp breaker with a 6mm wire leading to fused cooker switch. This then leads with 6mm cable to hardwire point. Can i hardwire 2 x...
Replies
11
Views
801
OLDBOY
O
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
676
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
921
Hi So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven . is this...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock