I visited a client about a week ago, an elderly couple complaining that their lounge, hall and landing lights were all flickering simultaneously with a noticeable buzzing noise. When I arrived the lights appeared to be working ok (I asked them to switch them off until I could attend), so an intermittent fault. Opening up accessories revealed the likely culprit - aluminium conductors, the first time I have come across these.

Some observations:
House built 1973
1mm² (or so I believe, next time I'll measure w/ micrometer) single solid strands
Dull silver appearance, brighter when cut.
Not copper clad aluminium, not tinned copper.
Very soft and supple compared to copper.
Higher resistance values vs copper
Prone to breaking off where screwed at the terminations.
It was hard to get a clean reading by testing continuity with the probe placed directly on the bare conductors (CPCs were unsheathed), the reading would jump around constantly in the range of a couple of ohms. I presume this is due to the insulating oxide layer aluminium is said to form. Clipping a jump lead to the conductor and testing to that gave a steady reading, as did testing to the brass terminal where soundly terminated.
Other circuits in the house are, at a glance, aluminium also.

I did what I could in the time I had available - I went through the circuit (downstairs lights) checking and tightening everything, found several conductors broken or very nearly broken at the screws so reterminated those, and ended up with satisfactory R1+R2 vs RN+R2 results. Borrowed neutral on landing light as you would expect for a property of that age.

Anyway, received another call from them on Christmas eve, they had noticed a small flash and pop! from one of the bedroom wall lights when switched on. Also switching on say the main bedroom light would cause a momentary flicker on the landing lights. He also told me they had an intermittent problem in the past with the bathroom light flickering, and certain sockets sparking when switched on. Advised not to use dodgy lights and sockets until I can get to them in a day or 2.

The place is obviously due a rewire, and that's what I will recommend. In the meantime, I'll need to make good any problems. I understand standard accessories are not to be used with aluminium conductors. Apparently some Wagos can be used on aluminium conductors when used in conjunction with the Alu-plus paste:


I was thinking of using this to connect a length of copper conductor to the ends of the aluminium conductors, then terminating the copper in the accessories. I have reservations though, I suspect the 1mm² aluminium will be too soft and bendy to force into a wago 773.

What have other members of the forum done in these circumstances and what would you recommend? As always, all information gratefully received :)
 
I can't remember any aluminium conductors so small in domestic.
Have you thought of ferrules for the terminations....a little substance to make them a bit more stable for the time being.
Good idea, ferrules would give them a bit of back-bone wouldn't they.

Yes, I'm wondering if they ever complied. I have a copy of 14th ed amended to 1976, there's a table of copper clad aluminium down to 1.5mm² but for plain aluminium, minimum is 16mm². I suppose it could have been different in previous amendments though.
 
Are the accessories, modern types? because if My memory serves me well, there was a Copper shortage back in the day and I seem to remember that the accessories, had to be redesigned to accept Aluminium conductors, I may be mistaken as it was back in my youth, and memories dull with the passing of time, may be some of the other old timers with a better memory, will clear things up.
The American Electricians do use some sort of gunk when they terminate Al conductors.
 
Last edited:
Are the accessories, modern types? because if My memory serves me well, there was a Copper shortage back in the day and I seem to remember that the accessories, had to be redesigned to accept Aluminium conductors, I may be mistaken as it was back in my youth, and memories dull with the passing of time may be some of the other old timers with a better memory will clear things up.
The American Electricians do use some sort of gunk when they terminate Al conductors.
I read that somewhere else too Pete. I'd say the hall and landing ceiling roses are probably original to the house, but switches have been replaced at some time or another, and the ceiling lights in the lounge are modern metal ones. You think the incompatible accessories are likely what's causing the issues?

The consumer unit was changed 2 or 3 years back. No mention of aluminium on the pre-change EICR, also no EIC or notification of the change. NICEIC approved contractor. I wonder if the MCB terminals are suitable for aluminium?
 
I read that somewhere else too Pete. I'd say the hall and landing ceiling roses are probably original to the house, but switches have been replaced at some time or another, and the ceiling lights in the lounge are modern metal ones. You think the incompatible accessories are likely what's causing the issues?

The consumer unit was changed 2 or 3 years back. No mention of aluminium on the pre-change EICR, also no EIC or notification of the change. NICEIC approved contractor. I wonder if the MCB terminals are suitable for aluminium?
If they have clamp type terminal they may be OK, it's the screw type that do the damage to Al conductors. my only memory is that Judas Escariot played in goal for Bethlehem Hotspurs.
 
Accessories are definitely screw type, all of them, even the old ceiling roses. Hager MCBs IIRC, so clamp type.
Yes Mate they will be better than screw type, still if that doesn't work, good for you but not your customer maybe a rewire is called for. Of course stripping Alum conductors with Side cutters wont help either, care needed to be taken so speed wasn't an issue, speed leads to errors and poor workmanship in most case.
 
I've never known aluminium cables that small, even the lighting cables all seem to have a much larger CSA than the copper equivalent. Best to rewire if you can, all the stuff I've come across has been very brittle, and broke off with very little amounts of bending.
 
Maybe a regional thing.
My parents house was built in ‘73 and it’s copper twin and earth, but the old stuff.
Ex council.

Have worked in old properties with VIR, but the insulation gave up well before the cable itself
 

Reply to 70s house, aluminium conductors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
671
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
723
The house I've just moved into is fitted with the light switches shown in the pics. They are fitted to each bedroom and the landing. The landing...
Replies
9
Views
957
My son is having a new house built. The electrical wiring is almost complete but a problem has been detected. Some of the rooms LED lights...
Replies
3
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top