Discuss 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
just been to a job , saw that the shower 9.5 kw is on 6mm t&e the cable goes in the wall and under floor boards ,No insulation, to the board (A cable run of no more than 10 m) . I said downgrade the shower to 8.5 max. Is it really necessary ? never quite sure , its borderline to me .
 
Should just about be OK so long as there is no insulation about but really CCC is about 38A and you are running 41A, clamp the circuit and see what it is pulling. Doesn't comply at the moment but no need to change if it is working without damage, they are only on for a short time (tin hat).
 
just been to a job , saw that the shower 9.5 kw is on 6mm t&e the cable goes in the wall and under floor boards ,No insulation, to the board (A cable run of no more than 10 m) . I said downgrade the shower to 8.5 max. Is it really necessary ? never quite sure , its borderline to me .

same here border line for me too i cant be arsed calculating it as others would slate it too
 
But 6 mm T&E can according to bgb can take 39a (I think without looking) and realistically the shower wont be pulling that (you could clamp it to see) therefor saying you should change the 6mm to 10mm is unneccessary (in my opinion). Doesn't matter that the MCB will take more than what it's rated at when the 9.5 kw shower wont be pulling more than the 40A
 
....and if the owner accidentally leaves it on......... all day ......

Seen it!

Personally don't know enough detail about how (and if ) a shower left on "full" cycles (or not). Is it like a kettle, full tilt for the duration? I suspect not.

Dunno.

If in doubt change.

My gut tells me it might get warm but would be ok as long as PD matches CCC of cable.
 
if it ain't broke, don't fix it. perfectly OK with a ccc of 47A on a 40A MCB.
 
New posts

Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
185
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock