When water is turned ON the RCD TRIPS.
10 metres from CU, 40A mcb. 10mm Doncaster Cable.
Changed to 50mcb and 25mm meter tails. still RCD trips?
 
I R test the element,
bet it has failed.

corrosion makes a small hole in element case and lets water in.
 
I thought he meant when he runs the tap !!

No wonder I was confused...
 
This is brand new Galaxy from Screwfix. This problem occurred. Could not find any faults so returned. It is only with replacement thatI query there cannotbe two faulty units, however, tests with multimeter all OK, so E TO L reads 0mV, so replace 10mm cable with 25mm meter tails and replace 40mcb with 50 mcb but that I agree is silly as it is an Earth leakage problem to switch the RCD.??
[automerge]1570181907[/automerge]
BTW, i have been installing CU, lighting and ring main circuits for 50 odd years. WHEN I had completed the whole circuit (I test each socket with SocketanSee) Then get friend sparkie to test and sign work off.
 
Last edited:
this is a simple element with a pressure switch to turn it on.
i still think that an insulation resistance test on the element will guide you to the problem.
 
Yes Zerax. Problem only occurs when tap is turned on.
[automerge]1570184669[/automerge]
I have placed the black cap on E and red cap on element. Testing with Multimeter between these two points reads 3M ohms
 

Attachments

  • AA007F27-EB66-48FA-ADD0-2A5B7BA2188F.jpeg
    1.6 MB · Views: 12
Last edited:
that is a poor result for a new appliance, a multimeter is only testing at very low voltage.
I expect that a 500V I R test between element and earth will give awful result. (disconnect incoming supply first)
 
Hi - as per James - safely isolate the circuit, disconnect the incoming L and N to the heater and confirm your results.
 
So I have returned to the unit black lead on end of element
Neutral) red on Earth 3 Mohms.
I then put Black on Earth red on Neutral 0.00 ohms
Massively confused, so I checking CU
same result N toE = 3M ohms
E to N - O.00 ohms
[automerge]1570189570[/automerge]
Disconnect Neutral to Galaxy. O/L reading on N to E or E to N.
Does this mean that there is fault in cabling to CU.
TOOK meter tails out of CU attached direct to Galaxy and it worked!,,,?
What the devil should I be suspecting.
 
Last edited:
I think at this point, you should be getting a local electrician involved.
 

Reply to 9.5kw Galaxy unvented heater trips RCD in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Shower circuit (40a mcb 10mm cable 8.5kw shower ) tripping after 5 mins RESET trips after 2 mins...changed shower /cable /isolator still tripping...
Replies
7
Views
593
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock