Discuss 9 Ohm L to N- 0.85 amps (157W). What's going on? in the UK Electrical Forum area at ElectriciansForums.net

P

p496hav

Hi guys

Just changed a board in a 60s bungalow, and whilst waiting for the customer to find the neon trashing my insulation readings, I checked low ohms live to neutral on an old 6mm radial with 7029 drops, socket circuit. Even in my head I worked out 9 Ohms equated to 23A or about 5Kw- Not possible, his bill would be ginormous.
Next day I plugged it into a power meter and got .85A or 157W. As he'd plugged stuff back in, that was perfectly acceptable, but I was still getting 17 Ohms.
I can't believe the cables are doing it as I'm getting 10meg cpc to L and N, so something is connected, what?
My mate thinks it's inductive or capacitive, and my meter is using dc to measure an ac load, but that's over my head.
Any ideas?
 
just follow your nose:

458456117_070.jpg
 
A switch neon
Ignition for a cooker
Fused down radial supplying any number of things like a fan
Anything with a transformer in it
Boiler control or timer

Basically you missed something when isolating all loads its always wise to Insulation test at 250v first when doing L/N to check for missed items as 500v can damage sensitive electronic equipment.
 
Inductive load, I'd concur. Transformer or motor, most likely. 9 ohms dc resistance as measured by your meter, but 270 ohms impedance at 50 Hz. Not capacitive though, that reads infinity to a dc resistance range.
 
Hi guys

Just changed a board in a 60s bungalow, and whilst waiting for the customer to find the neon trashing my insulation readings, I checked low ohms live to neutral on an old 6mm radial with 7029 drops, socket circuit. Even in my head I worked out 9 Ohms equated to 23A or about 5Kw- Not possible, his bill would be ginormous.
Next day I plugged it into a power meter and got .85A or 157W. As he'd plugged stuff back in, that was perfectly acceptable, but I was still getting 17 Ohms.
I can't believe the cables are doing it as I'm getting 10meg cpc to L and N, so something is connected, what?
My mate thinks it's inductive or capacitive, and my meter is using dc to measure an ac load, but that's over my head.
Any ideas?

Shouldn't you be doing this?
 

Reply to 9 Ohm L to N- 0.85 amps (157W). What's going on? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi all, I’m hoping you can shed some light on a problem I found. Please be gentle, I’m an industrial spark, not a domestic spark. I’ve been...
Replies
8
Views
2K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi all, been called out to a job today where the customer says they are getting a tingle from the gas meter and some appliances. Its a TT system...
Replies
33
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock