CDB
-
- Reaction score
- 10
Hi everyone,
I have my 94/95 practical assessment on Tuesday and am a little confused about the sequence of tests. Basically I don't want to screw it up just because I do them in the order that they are not looking for. The 94 element I'm pretty happy with -
- Assessment of general characteristics
- Continuity of protective conductors, including protective bonding
- Continuity of ring final circuit conductors
- Insulation resistance tests
- Polarity dead tests
- Polarity live tests
- External Earth fault loop impedance (Ze)
- Prospective fault current test (PSCC and PEFC)
- Earth fault loop impedance (Zs)
- Phase sequence test
- RCD test
- Functional testing
But for 95 we have been advised by our lecturer at the same centre as the assessment:
- Assessment of general characteristics / site survey etc.
- LIVE
The suggest here is that Zs tests at sockets and light switches will tell us if we have continuity of CPC and Functional will tell us if we have working systems. Would you use a socket&see to test 'function' of a socket?
Has anyone else seen this for 95 practicals?
Look forward to your replies and thanks for your time.
Chris
I have my 94/95 practical assessment on Tuesday and am a little confused about the sequence of tests. Basically I don't want to screw it up just because I do them in the order that they are not looking for. The 94 element I'm pretty happy with -
- Assessment of general characteristics
- Continuity of protective conductors, including protective bonding
- Continuity of ring final circuit conductors
- Insulation resistance tests
- Polarity dead tests
- Polarity live tests
- External Earth fault loop impedance (Ze)
- Prospective fault current test (PSCC and PEFC)
- Earth fault loop impedance (Zs)
- Phase sequence test
- RCD test
- Functional testing
But for 95 we have been advised by our lecturer at the same centre as the assessment:
- Assessment of general characteristics / site survey etc.
- LIVE
- Functional testing (inc RCD test?)
- Earth fault loop impedance (Zs)
- DEAD- Earth fault loop impedance (Zs)
- Insulation resistance test - whole installation and then circuits to fault find.
- External Earth fault loop impedance (Ze)
- Prospective fault current test (PSCC and PEFC)
- Then CPC etc. as and when required to fault find.
- External Earth fault loop impedance (Ze)
- Prospective fault current test (PSCC and PEFC)
- Then CPC etc. as and when required to fault find.
The suggest here is that Zs tests at sockets and light switches will tell us if we have continuity of CPC and Functional will tell us if we have working systems. Would you use a socket&see to test 'function' of a socket?
Has anyone else seen this for 95 practicals?
Look forward to your replies and thanks for your time.
Chris