A good guide For 'exported PME' and outbuildings!

Discuss A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Reaction score
1,512
For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.

It was published in 2005 but the important bits remain unchanged and might be of some help!
 

Attachments

  • Garage-Shed Supplies.pdf
    243.4 KB · Views: 5,858
This really needs to go back in the ''Sticky section'' above!! It seems that there are still far too many here, that have been brainwashed by the scaremongers into believing you can't extend a PME equipotential zone, or take a PME CPC with you to an outbuilding or shed!!
 
Hi, great thread - quick question... I'm installing power and light to a workroom in the back of a detached barn. Supply is off a spare way in the house and will feed a small consumer unit in the barn. The barn cu will have 30ma RCDs so my question is: Am I right to use a 100ma RCBO at the house so the whole thing doesn't automatically trip?
 
Hi, great thread - quick question... I'm installing power and light to a workroom in the back of a detached barn. Supply is off a spare way in the house and will feed a small consumer unit in the barn. The barn cu will have 30ma RCDs so my question is: Am I right to use a 100ma RCBO at the house so the whole thing doesn't automatically trip?

Also, there is a strong possibility that the 100mA at the house will trip at the same time as to 30mA in the barn. You will need a time-delayed (s-type) RCD in the house if you want to provide discrimination whilst protecting the supply cable. Not sure whether you are an electrician or not, so just to let you know, this job would be notifiable to your LBC.
 
As Guitarist said, the 100mA device will almost certainly trip simultaneously with a 30mA device downstream-does this 'supply cable' actually REQUIRE RCD protection?
 
I think we are now entering the realms of competency here ....................... I will hand you over to my learned friends I think

You are not talking circuit breaker but RCD protection, but even if not then the type of circuit breaker is very relevant and is certainly linked with Zs values.
 
Ah, just noticed all the other replies, sorry guys, my first time here. Yes I am an electrician, qualified 2yrs ago but this job isn't my usual bag. Yes the cable does require RCD protection as it will be supplying power for outdoor use. The installation in the barn is entirely fitted in conduit.
 
Ah, just noticed all the other replies, sorry guys, my first time here. Yes I am an electrician, qualified 2yrs ago but this job isn't my usual bag. Yes the cable does require RCD protection as it will be supplying power for outdoor use. The installation in the barn is entirely fitted in conduit.

That in itself is not a requirement for RCD protection of a distribution circuit.
 
Thanks, but some of us have been taught that the DNO will not accept that on a TNC-S system. I am not trying to be contentious here but wonder where that myth came from.

From bias lectures that don't like PME earthing!! That seems to be one of the biggest influences anyway!! Same goes for RFC's, Using the Armour of SWA cables as the circuits CPC, and a few others too boot as well...lol!!
 
What another cracking thread. So in summary so I can go forward,

1) We can export if practicable, if not TT it with all the usual requirements.

2)If we do export then a 10mm Main bonding cable must be provided, if services enter the location

3) If the CSA of the supply cable is <10mm we must provide a separate Main bonding conductor of 10mm

4)If the supply cable CPC CSA is > 10mm or + we can use said CPC as our 10mm main bond


Have I missed anything ?

My understanding from gn8 IS your exported bonding coductor size is the same as you bonding conductors for your main installation so if your main bonding is 50mm then your bonding to your outbuilding/shed will be 50mm even if your supply conductor size is only 16mm(to the out building)
 
My understanding from gn8 IS your exported bonding coductor size is the same as you bonding conductors for your main installation so if your main bonding is 50mm then your bonding to your outbuilding/shed will be 50mm even if your supply conductor size is only 16mm(to the out building)

Yes, the main protective bonding conductors on a PME system are sized in accordance with the SUPPLIERS neutral conductor (not the tails) and as you rightly say, there is no provision to reduce the size in a distribution circuit to another building with main protective bonding requirements.
 
I'm just bumping some of the older threads in the general electrical forum that had a lot of replies. They might not be current topics, if they're not, just ignore them and they'll soon drop off the list. If you DO wish to add a reply and get the conversation going again, feel free to do so. Your input might help somebody else in the future.
 
New posts

Reply to A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock