Whilst the cabling is adequately protected at 13A, the vast majority of manufacturers have always specified a 3A fuse to protect the boiler. Also - whilst it might be 1.5mm conductor size at the start, consider the rest of the system downstream of that such as 2 ports, timers etc all of which can often have much reduced cable sizes.
 
Howcomes we use eg a 3a fuse from the FCU to feed a boiler that has 1.5mm wiring? Wouldn't a 13a still be ok and if not, why not?

TIA

The process for selecting the size of fuse required is to assess the design current, which for a small/domestix boiler will be less than an Amp, then to select the nearest standard size fuse, which would be 3A.

We also have to take account of manufacturers instructions which will state that a 3A fuse is required for a gas boiler and usually a 5A fuse for an oil boiler.

Boiler wiring will also usually be 0.75mm as anything bigger is not required.
 
MI will usually state 3amp or 5amp fused for most boilers , so a bit or 1mm flex would do the job.
Using anything larger is just a waste of money really
This is something not seen much today but the UK system with 3A/5A fuses could support 0.5mm flex quite safely, where as the EU/USA/world system of unfused plugs means the flex has to cope with the I2t of something like 16A OCPD at the distribution board.

Of course now the copper saving cost is dwarfed by the desire to make products for multiple markets, so you find nothing below 1mm/0.75mm made as a result, even for small loads, as the UK market is small compared to all of those combined.
 
This is something not seen much today but the UK system with 3A/5A fuses could support 0.5mm flex quite safely, where as the EU/USA/world system of unfused plugs means the flex has to cope with the I2t of something like 16A OCPD at the distribution board.

Of course now the copper saving cost is dwarfed by the desire to make products for multiple markets, so you find nothing below 1mm/0.75mm made as a result, even for small loads, as the UK market is small compared to all of those combined.
Also easy to forget that most of the decent DB manufacturers also make 3A MCB's
 
This is something not seen much today but the UK system with 3A/5A fuses could support 0.5mm flex quite safely, where as the EU/USA/world system of unfused plugs means the flex has to cope with the I2t of something like 16A OCPD at the distribution board.

Of course now the copper saving cost is dwarfed by the desire to make products for multiple markets, so you find nothing below 1mm/0.75mm made as a result, even for small loads, as the UK market is small compared to all of those combined.
I come a lot of appliances these days come supplied with 1.25mm flex , presumably as this is the smallest ( cheapest ) sized flex for 16amp appliances around the globe
 
Also easy to forget that most of the decent DB manufacturers also make 3A MCB's
True, the the fault I2t of such an MCB is usually way higher than a 3A fuse, except in the region just after the magnetic trip.

E.g. typical Hager 3A MCB has about 70 A2s of let-through at 100A fault current, 3A BS1362 fuse at that point is worst-case specification is around 15 A2s (slope implying in the constant I2t sort of region) and probably less, so almost 5 times less.

Higher up at 2kA fault the MCB let-through is around 3 kA2s but fuse still offering about 15 A2s and now the fuse is around 200 times less.
 
Whilst the cabling is adequately protected at 13A, the vast majority of manufacturers have always specified a 3A fuse to protect the boiler.
As far as I am aware manufacturer,s only seem to get away with this in Ireland and the UK only.In other countries manufacturers are expected to take care of this issue themselves by fusing the appliance internally
 
One issues is if both the permanent and switched lives both need fused. Really someone should slap down on this and say that anything falling in to those categories has to be designed as safe with a 6A MCB.

I've fitted maybe two dozen fans in the last couple of years and all were safe on a 6A circuit.
 
One issues is if both the permanent and switched lives both need fused. Really someone should slap down on this and say that anything falling in to those categories has to be designed as safe with a 6A MCB.

Absolutely. And it shouldn't be difficult to be honest. Let's face it, most fans will be fine on a 6A device - it's just some over cautious manufacturers covering themselves.
 
If you look inside the motor's wire will blow before a 3A fuse, and that won't stop it overheating if locked either locked rotor current is going to be fraction of an amp. So really is is just looking for a weasel way out of any claims...
Thats a very interesting point .It would explain why these very same fans are installed all over the continent and are protected ,not by a 3 or 5 amp fuse ,but by the 16 amp circuit mcb.
 

Reply to A thought about fuses in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
699
From another thread: I'm thinking about this and it's got me all confuzzled. Don't fuses protect anything downstream ie my laptop's charger...
Replies
16
Views
2K
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
852
Hi ive recently got myself a mig welder for my garage but each time i try to use it it trips out. Ive spoken to an electrician and he said its...
Replies
25
Views
699
Apparently Dimplex only guarantee their heaters if they are permanently wired in to a fused outlet. If the socket is only about 600mm from the...
Replies
5
Views
411

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock