Hi Everyone , I am new to this forum. Infact its my first time ever being on any kind of forum.
I need your help on a very basic concept of electrical circuits that is confusing me alot and has shattered my basic concepts.

The question is :
In circuits we often tend to ground the negative terminal of a battery ( DC ). So the positive terminal is at higher potential.
Why do we connect FUSE on the positive terminal side & why do we connect LOAD on negative terminal side.
Because the direction of electronic current is still from negative terminal to positive terminal. So the fuse should have been on the negative terminal side of a battery.
 
are you referring to vehicle electrics?
 
The negative path in a vehicle can be through any and all bodywork metal so it would be impossible to ensure that the fuse is in the circuit if it was inserted into the negative as much of the current could bypass the fuse
 
If the fuse was on the Negative side and operated it would leave the circuit live still with a PD to ground... putting it on the positive side ensure tht when a fuse operates the associated circuit has no potential to negative/ground in your example removing the risk of shocks or fires from possible faults, the shock risk is minimal when discussing SELV (safety extra low voltage) like found in cars etc for instance but you would still want the fuse to de-energise the circuit with reference to ground.
 
The fuse would have to be at the component , It would mean that fusing at a central point such as a 'fuse box' would be very costly to manufactures as it would mean double wiring.

Older cars had live chassis.
 
@darkwood - but wont the current pass through the load first when we place it on negative side which means if there is any fault i-e any high currents ( short circuits ) the current would pass through the load before it could pass through fuse. Making the load vulnerable to damages ?
 
@telectrix - the video i was watching was about cars but my question is a general question. Just like in any electrical schematic we see a fuse connected to a hot wire ( in series to a source ). Whose basic purpose is the safety of equipments. But as the current flows from neg to pos in DC why dont we connect a fuse on negative terminal side ?
 
It doesn't matter from a current flow point of view where the fuse is, it breaks the circuit and stops the flow of current wherever it is.
The same current flows throughout the whole circuit up to the point at which the fuse blows
 
@darkwood - but wont the current pass through the load first when we place it on negative side which means if there is any fault i-e any high currents ( short circuits ) the current would pass through the load before it could pass through fuse. Making the load vulnerable to damages ?

I build controls systems so I spec' to different regs than that of vehicles so are we assuming we are discussing vehicles here as you never said the scenario.
If we are discussing cars then removing the raised potential against the chassis is safer and when you say a fault would go through a load then why if it was say a short before the load to the chassis it wouldn't flow through the load as it follows the path of least resistance.

You fuse the section where the raised potential would be against the common or ground (chassis) be it strapped + or - design.. A battery at the end of the day is eg 12v and it doesn't matter which side you strap to the chassis by design the feed side of all the loads becomes the raised potential against the chassis be it positive or negative source and its this that needs fusing to ensure all potential (with respect to the ground/chassis) is removed from the wiring in a fault or overload condition.
 
Last edited:
Davesparks - the current would pass through the load first which if very would damage the load ( and most of the power would be lost ) which means less current will flow through the fuse making the fuse worthless ..
 
Davesparks - the current would pass through the load first which if very would damage the load ( and most of the power would be lost ) which means less current will flow through the fuse making the fuse worthless ..

No it won't, the current passes through the whole circuit at the same time. Current does not diminish, get used up or lost throughout the circuit. The total current flowing out from the negative terminal of the battery will return via the positive terminal of the battery.
 
As above, the fuse is in whichever side of the circuit is not connected to the common or grounded terminal of the supply. This is because modern practice dictates that we ground the neutral so reliably, that there is negligible chance of it becoming live with respect to true ground, hence no need to fuse it. It does not matter whether it is positive, negative or one side of an AC supply, the fact it is solidly grounded avoids the need for a fuse. Single-pole fusing in the line / 'hot' side only, gives the benefit that when a fuse fails it will always disconnect the load from the 'hot' side.

So in household single-phase AC supplies in the UK, that's the line conductor (the neutral is grounded). In modern cars it's DC positive as the negative is grounded i.e. connected to the chassis (for compatibility with electronics), although historically the positive was grounded and fuses were in the negative.

If neither side of the circuit is grounded, then all conductors must be fused. Examples include domestic 240V circuits in the USA (which are centre-tapped to ground, making both sides hot at 120V), and single-phase circuits derived from 3-phase delta, such as shipboard power and historically in mainland Europe for domestic supplies, which also have neither side grounded and must be fused in both lines.
 
@Lucien Nunes - Your detailed reply is really appreciable and helpful to me. You described it in really simple words [emoji106]

But what If a short occurs at the positive side of a battery before the fuse ? Wont a very large current pass through load because the load is on negative side and there is no fuse on its side ?
 
I mean the very basic purpose of fuse is to protect the load from overloading. So a short on positive side right after the load would cause a large current to flow through the load and could eventually destroy it. Even a short on positive side of battery would cause fire as there is no fuse there at all ?
 
I mean the very basic purpose of fuse is to protect the load from overloading. So a short on positive side right after the load would cause a large current to flow through the load and could eventually destroy it. Even a short on positive side of battery would cause fire as there is no fuse there at all ?

No, the fuse is there to protect the wiring from the effects of faults and overloads.
Any protection required for the load itself will be provided at the load (in/on the piece of equipment.

A short circuit is by definition a fault which causes the flow of current to bypass the load (thus in very simple terms the circuit is shorter than it should be)

The impedance of the load will determine the amount of current which flows in normal operation,
 
Kirchoff's Law springs to mind.

250px-Walter_Koenig_Star_Trek.JPG
:punk:
 
@davesparks - yes , you are right. I just confused it entirely. A short ryt after the load ( i-e positive side wire with the negative side wire will bypass the load and the fuse will blow so no current passes through load.

But a short before the load that is on negative side still will cause fires ( damages to wire ) because there is no fuse in that side ?
 

Reply to A very basic thing in electrical circuits that has confused me for weeks in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Once again I am using the Engineering chat as I think my question is more theoretical rather than 'diy advice'. If I am misusing the forum...
Replies
17
Views
2K
I have an 5kW inverter and 48V Lithium battery with inbuilt BMS. As you would be aware, when inverter gets battery power, immediately the...
Replies
0
Views
550
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
897

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock