- Reaction score
- 2,853
Browsing the OSG, I notice in section 7 that the data for ring finals assumes the load is distributed throughout the circuit, whereas the data for 20A and 32A radials assumes a terminal load.
So my question (particularly to those who install radial socket circuits regularly, in preference to rings):
When calculating voltage drop for A2 and A3 radials powering sockets, how are you treating the load: as if all the load is at the terminal point of the circuit, or as if it is distributed throughout the circuit? And if the latter, how do you assume it is distributed?
So my question (particularly to those who install radial socket circuits regularly, in preference to rings):
When calculating voltage drop for A2 and A3 radials powering sockets, how are you treating the load: as if all the load is at the terminal point of the circuit, or as if it is distributed throughout the circuit? And if the latter, how do you assume it is distributed?