UK AC RCD’s C2? Absolutely!

Discuss AC RCD’s C2? Absolutely! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Given the advancement in technology and the high amount of potential DC in electrical systems. An AC RCD that won’t work, invokes so many further regulations for circuits that need RCD protection that no longer do! 100% C2 in my opinion
 
You might be able to make such a case for specific installations, but as a blanket statement I'd imagine it would be dificult to back up.

How would you justify coding every Type AC RCD as "Potentially dangerou’. Urgent
remedial action required"
?

What potential danger exists in the average home with Type AC protection?
 
You might be able to make such a case for specific installations, but as a blanket statement I'd imagine it would be dificult to back up.

How would you justify coding every Type AC RCD as "Potentially dangerou’. Urgent
remedial action required"
?

What potential danger exists in the average home with Type AC protection?
The AC RCD is essentially rendered useless due to DC current. So off the top of my head circuits within a bathroom, sockets supplying external equipment, electric showers, cables in walls less than 50mm from the surface…all require RCD protection in a standard home, however if the RCD doesn’t work, how is that not potentially dangerous? I wouldn’t like to be the one justifying my case to the man in the wig over this one!
 
The AC RCD is essentially rendered useless due to DC current. So off the top of my head circuits within a bathroom, sockets supplying external equipment, electric showers, cables in walls less than 50mm from the surface…all require RCD protection in a standard home, however if the RCD doesn’t work, how is that not potentially dangerous? I wouldn’t like to be the one justifying my case to the man in the wig over this one!

Can you clarify if you mean an RCD that won't work as it has failed or an RCD that won't work due to DC current injected by a downstream appliance?

I may have grasped the wrong end of this particular stick, but in my defence your OP is open to misinterpretation and thread title suggests blanket C2 for Type AC protection.
 
Can you clarify if you mean an RCD that won't work as it has failed or an RCD that won't work due to DC current injected by a downstream appliance?

I may have grasped the wrong end of this particular stick, but in my defence your OP is open to misinterpretation and thread title suggests blanket C2 for Type AC protection.
An RCD that won’t work due to DC current injected downstream! Apologies, I wouldn’t say a blanket C2 but certainly more common than not in my opinion
 
Yes, that’s essentially my point. I’m seeing a lot of people pass over this issue with AC rcds and not even bother coding it. It’s a major issue that’s being ignored by too many!

A failed RCD needs to be replaced, regardless of type of protection provided. I've never encountered anyone who would ignore failed RCD protection.
 
If you read the Best Practice guide #4 for EICR coding (Nov 2022) from Electrical Safety FIrst, it states for "A Type AC RCD installed where a Type A RCD required" to be coded as C3.
It also says that coding is entirely at the discretion of the inspector and the document is merely a guide. I would rather be fussy and improve a system than be lazy and have someone’s death on my conscience. Honest question, if you know an AC rcd may not work in a fault situation, explain why you would code it as a C3 and negate the need for someone to fix it. Imagine a child sticks their finger in a lamp holder? But the rcd fails…
 
It also says that coding is entirely at the discretion of the inspector and the document is merely a guide. I would rather be fussy and improve a system than be lazy and have someone’s death on my conscience. Honest question, if you know an AC rcd may not work in a fault situation, explain why you would code it as a C3 and negate the need for someone to fix it. Imagine a child sticks their finger in a lamp holder? But the rcd fails…

A short while back we established that you were commenting on failed units, but now the conversation seems to have shifted to RCDs that 'may not work in a fault situation'.

How are you establishing that an RCD may fail to operate?

As for coding being at the discretion of the inspector, that's the sort of argument applied by testers who blanket code insulated CUs as C2.

Coding should be back up by regulations and sound engineering judgement. It should not be whimsical in nature.
 
Last edited:
A short while back we established that you were commenting on failed units, but now the conversation seems to have shifted to RCDs that 'may not work in a fault situation'.

How are you establishing that an RCD may fail to operate?

As for coding being at the discretion of the inspector, that's the sort of argument applied by testers who blanket code insulated CUs as C2.

Coding should be back up by regulations and sound engineering judgement. It should not be whimsical in nature.
It’s common knowledge that DC current in a circuit with an AC RCD impairs it’s ability to work. Domestic properties have numerous electrical items, induction hobs, led lighting, EVCP’s that all can present this within an installation. There are loads of videos on YouTube explaining the logic behind it. It’s in the regs check out 531.3.3! As for sound judgement I’m an electrical technician with an electrical engineering degree and twenty years testing experience. I think I’m suitable to make the decision. There is a reason they are banned in half the world!
 
It’s common knowledge that DC current in a circuit with an AC RCD impairs it’s ability to work. Domestic properties have numerous electrical items, induction hobs, led lighting, EVCP’s that all can present this within an installation. There are loads of videos on YouTube explaining the logic behind it. It’s in the regs check out 531.3.3! As for sound judgement I’m an electrical technician with an electrical engineering degree and twenty years testing experience. I think I’m suitable to make the decision. There is a reason they are banned in half the world!

Yet for most of those 20 years you were completely unaware of the issue, until Youtube broadened your knowledge?

I was hoping for an explanation of your testing process, rather than coding on the basis of assumption and that's the problem I have with this sort of blanket coding. 'Potential' exists for failure of Type A RCDs. Where they are used for fault protection, do you mandate that additional protection be provided on the basis of 'what if'?

While I don't disagree with the basic premise that Type A protection would be preferable, I do disagee with the idea of coding on the basis of assumption where no potential danger can be demonstrated in a particular installation.

A failed RCD needs to be replaced, regardless of whether that failed unit is Type AC, A or other. A working RCD does not need to be replaced, unless evidence exists to suggest that it will fail to operate (whether that be for the reasons you outline or for any other reason). The average house does not have an induction hob or EVCP and basic LED lamps aren't likely to introduce sufficient DC current to prevent operation of a Type AC RCD. In short, while it may be the case that Type AC protection isn't suitable for a modern installation, most homes do not possess what might be considered a 'modern installation'. Coding should be appropriate to each installation inspected.
 
I'd like to qualify my previous comments as the OP probably knows nothing about me and might consider them to be argumentative or harsh. The comments weren't intended to be either, but as an apprentice I find myself disappointed and frustrated when no logic is apparent behind blanket statements.

We're all entitled to our opinions, but equally we should be able to substantiate them as bold opinions are likely to be challenged.

Tl;dr... No offense intended, but I want to learn and want to do so in an informed manner.
 
Honest question, if you know an AC rcd may not work in a fault situation, explain why you would code it as a C3 and negate the need for someone to fix it.

If the RCD is there for additional protection then it is possible that it should be a C3 as it is additional protection and not the primary protection which is potentially compromised.

If there is a definate, confirmed presence of DC leakage currents which will alter the operation of a type AC RCD then that is a different story to guessing that there maybe might be an issue.

Imagine a child sticks their finger in a lamp holder? But the rcd fails…

An RCD is unlikely to assist in that situation anyway. If a child sticks their finger in a lampholder then they are more likely to make contact with both the live and neutral, this will result in current flowing through their finger which the RCD will see as normal load current.
 
If you read the Best Practice guide #4 for EICR coding (Nov 2022) from Electrical Safety FIrst, it states for "A Type AC RCD installed where a Type A RCD required" to be coded as C3.
Indeed they do, but I must admit I find this suggestion somewhat questionable. Surely if an RCD is required, and the circumstances of the installation dictate that it needs to be a minimum of a Type A RCD because a Type AC RCD could be disabled by circulating DC currents then a C3 Observation seems overly lenient. But alas, you are correct that this is what that Best Practice Guide suggests.
 
It’s common knowledge that DC current in a circuit with an AC RCD impairs it’s ability to work. Domestic properties have numerous electrical items, induction hobs, led lighting, EVCP’s that all can present this within an installation. There are loads of videos on YouTube explaining the logic behind it. It’s in the regs check out 531.3.3! As for sound judgement I’m an electrical technician with an electrical engineering degree and twenty years testing experience. I think I’m suitable to make the decision. There is a reason they are banned in half the world!
Common knowledge indeed, but one thing that remains mostly unanswered is how the DC current comes to be passing through the RCD in the first place? Presumably a circuit must be completed for it to flow, so is it deliberate, or is it due to faulty equipment? And what route does it take? Any answers (with sources) appreciated
 
Another reg that I think is daft and has been changed for changes sake. I would have thought that in 99% of situations an AC RCD will be just fine, certainly in all the EICR's that I've done over the last few years and all the installations that I've done with AC ones they all tripped off no problem under test, the ones that didn't were physically faulty (BG ones for eg) despite houses being full of LED lamps, TV's, phone chargers, HOB's, washing machines etc etc.

My house is a perfect example, I have lots of electonic goods, your typical house, probably more so with my computer stuff, yet the 10 year old RCD trips off every time the oven is on for more than 30 minutes, its needs a new element.

From what certain people are saying I have a C2 problem in my consumer unit which is potentially dangerous, no RCD at all would be a C2 as well, so going by that logic I might as well ditch the RCD altogether and be no less safe than I was before, then I could have a roast dinner and not just a pizza.
 
Another reg that I think is daft and has been changed for changes sake.
It has been changed because the older RCD technology is no longer appropriate in a modern installation.
I would have thought that in 99% of situations an AC RCD will be just fine, certainly in all the EICR's that I've done over the last few years and all the installations that I've done with AC ones they all tripped off no problem under test
Tripping under test conditions is different to tripping under real world conditions.

My house is a perfect example, I have lots of electonic goods, your typical house, probably more so with my computer stuff, yet the 10 year old RCD trips off every time the oven is on for more than 30 minutes, its needs a new element.

I think you've misunderstood some basics here.
The RCD tripping due to a faulty oven element does not prove whether or not it has been affected by any DC leakage.
 
Common knowledge indeed, but one thing that remains mostly unanswered is how the DC current comes to be passing through the RCD in the first place?
DC leakage occurs from electronic loads, especially switch mode power supplies and the like.
Presumably a circuit must be completed for it to flow, so is it deliberate, or is it due to faulty equipment? And what route does it take? Any answers (with sources) appreciated

Lucien wrote a pretty good explanation of the DC leakage subject relatively recently. It should be possible to find it with a search.
 
It has been changed because the older RCD technology is no longer appropriate in a modern installation.

Tripping under test conditions is different to tripping under real world conditions.



I think you've misunderstood some basics here.
The RCD tripping due to a faulty oven element does not prove whether or not it has been affected by any DC leakage.
Well if it has been affected by DC leakage then it still tripped so all is good and if it hasn't been affected by DC leakage then all is good too. My house has all the possible scenarios that could cause DC leakage but the RCD still trips merrily away.
 
It’s common knowledge that DC current in a circuit with an AC RCD impairs its ability to work. Domestic properties have numerous electrical items, induction hobs, led lighting, EVCP’s that all can present this within an installation. There are loads of videos on YouTube explaining the logic behind it. It’s in the regs check out 531.3.3! As for sound judgement I’m an electrical technician with an electrical engineering degree and twenty years testing experience. I think I’m suitable to make the decision. There is a reason they are banned in half the world!
Sorry on behalf of everyone else we didn’t realise you had a degree, I’ll be the first to bow down to you. Our years practical experience working on site years means nothing when the piece of paper enters the room.
 
I think there are valid points on both sides of this debate.

In general if an RCBO seems to work (and I usually try a type A test too even though it isn't required) then I feel I have no evidence that it isn't doing it's job, and it's a C3.
In practise I find most Type AC RCBO's will trip if tested on a Type A setting, and normally within required times. (Using the x5 test they sometimes didn't quite make 40ms but only by a few ms.). So far the only ones that didn't trip also didn't trip on a type AC test because they were stuck or broken.

If you remember the older No Trip loop testers used to used DLOK and deliberately inject DC to blind the RCD, and it's telling that this technology had to be abandoned as it fails to work on almost all RCBOs.

In general I'm more concerned about older shared RCD's where the cumulative DC leakage from multiple circuits can be higher, and the older ones seem to be more susceptible to DC blinding in the first place (backed up by the fact that older loop testers could successfully 'fool' them).
I'd love to get a DC leakage clamp meter to help make better informed decisions but it hasn't made it to the top of the wish list yet.
 

Reply to AC RCD’s C2? Absolutely! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock