I hope i can word this so it makes sense...
When testing for instance a ring final for RCBO tripping times, is the test voltage within the test instrument reduced to 50Vmax to simulate the max permissable touch voltage? ie, is there a 1667 ohm resistor inside and 50 volts applied across it so 30ma can flow and then times taken etc,etc?

Thanks
 
There isn't a test voltage per se.
The instrument uses the supply voltage, and then places differing resistances between the L&N conductors to produce various loads.
When conducting a ramp test, the instrument starts at maximum resistance, and then decreases the resistance untill the RCD trips.
 
There isn't a test voltage per se.
The instrument uses the supply voltage, and then places differing resistances between the L&N conductors to produce various loads.
When conducting a ramp test, the instrument starts at maximum resistance, and then decreases the resistance untill the RCD trips.
Would that mean that in proportion to 50v/1667ohms= 30ma
the instrument would now apply 230v/7668ohms= 30ma ?
 
Hi Spin,

There isn't a test voltage per se.
The instrument uses the supply voltage, and then places differing resistances between the L&N

I thought this test was done between L&E, with the E being the variable ( as in different or unknown on each installation) lower half of a Potential divider, the tester being the upper half, and as you say it decreases the resistance values of the upper part of the potential divider until the required current flows, that is why if you have a crap earth (High resistance), if the upper part of the potential divider reaches a certain low enough resistance value WRT earths resistance value, ie. leading to =>50V (using ohms law) at the Potential dividers junction, the tester will inhibit the test, to stop the earths voltage rising any further up to dangerous levels, ie. higher than 50V

I hope this makes sense, I know what I mean, but it is difficult to get across in words Lol
 
Last edited:

Reply to Actual test voltage using RCD tester? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
287
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
886
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi folks. Im a RECI contractor based in Co Sligo, Ireland . I was doing erroneous testing on a domestic board which gave me readings between 90V-...
Replies
14
Views
2K
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock