Discuss Add 13a socket to cooker circuit? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi, The current state of play is a standalone combined oven and hob supplied by single cooker circuit with 40A RCBO, 6mm cable, isolated by cooker control switch and the unit is hardwired to cooker connection unit.

The plans are to change to built in oven and separate hob. The supply demands are not changing drastically so the installation needs no alterations apart from the new oven is fitted and protected by 13A plug and the new hob needs to be hardwired.

My thoughts are to extend the circuit leaving the connection unit in place for the hob and add a single 13A socket or FCU for the oven.

What are your thoughts? Is this reasonable?

Thanks in advance.
 
Can you simply use a cooker switch/outlet that has a single 13A socket for a kettle, etc?

Electrically what you propose seems fine, assuming the related terminals can accept the 6mm cable in and another short length of cable to the single socket/FCU out, but worth ensuring the socket/FCU is clearly lables as part of the cooker circuit.
 

Reply to Add 13a socket to cooker circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
641
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
805
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock