Discuss Add motion sensor to one light in bathroom in the Lighting Forum area at ElectriciansForums.net

lifesigns

DIY
Reaction score
0
Hi,

Some advice would be appreciated…

I have 4 downlights in the bathroom and want to add a motion sensor to turn on just one if everything is off.

If I turn on the light switch I want all 4 to come on until it’s turned off again.

Thanks,

Shane
 
Hi,

Some advice would be appreciated…

I have 4 downlights in the bathroom and want to add a motion sensor to turn on just one if everything is off.

If I turn on the light switch I want all 4 to come on until it’s turned off again.

Thanks,

Shane
I would avoid using a contactor.
A 3 position 2 pole switch would work.

Centre would be off
Down would be all lights on
Up would be one lamp via the sensor.

Or you could use a 2 way 2 gang one feeding all the lights and the other feeding one via the sensor.

Both up would be off
One down would be one lamp via the sensor
Other would be all lights on.

Or you could use one 2 way switch.
L1 would be lamp via sensor
L2 would be 3 lamps

There would be no off, but you could have an isolator switch elsewhere.
 
Last edited:
I've thought about doing this in my bathroom, its harder than it seems, just like you I want 4 downlights to work as normal via a dimmer switch but if the lights are switched off I still want one of them to operate via a sensor but still come on quite dim. I'm sure it can be done with a couple of contactors and dimmer switches but the only time I think about it is just after I've gone for a pee in the middle of the night.
 
put in a fifth downlight which is only on the sensor.... which works whether the other four lights are on or off.
Some of the hotels I stay in have this but the sensor light is a blue LED light. It's light enough so that you can see what you are doing (and not pee over the floor) but dim enough not to blind you when you've just got up in the middle of the night.
 
put in a fifth downlight which is only on the sensor.... which works whether the other four lights are on or off.

simples

most sensors have a dusk to dawn setting as well, so if the other lights are on, the sensor shouldnt operate.

Mine is something similar. Normal downlights on a light switch, and then some small lights set into the tiles which come on when a movement sensor is triggered. Nice easy way of getting a small amount of automatic light for a night time pee, and full lighting if required.

Dead easy, no contactors or complex wiring.
 
Some of the hotels I stay in have this but the sensor light is a blue LED light. It's light enough so that you can see what you are doing (and not pee over the floor) but dim enough not to blind you when you've just got up in the middle of the night.

Stayed in a hotel recently with an amber light under the basin at night. Great choice of colour when trying to not fully waken during those middle of the night trips to the bathroom.
 
I don’t actually think about lighting or waking anyone else when I’m bursting for a p@@ 🤣

Oddly enough, busting to pee is the reason I'm reading this thread.

Certainly didn't think about wiring at the time, but light from outside wakened me sufficiently that I didn't fall back asleep and here I am reading about wiring.

Thinking it was Monday and being late for work probably didn't help😩
 
While I appreciated the warm, low colour in that recent hotel, I much prefer to move about in the dark at night. My father is the polar opposite with nightlights all over the house - both battery and mains, with perhaps three working at any one time in hall, kitchen, utility room, landing and bathroom. Nothing worse than calling with them during darker months and be blinded by some bloody spotlight as you walk through the door.
 

Reply to Add motion sensor to one light in bathroom in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Can I use multiple GU10 led lamps with their own PIR sensors in the same room? I have a row of existing lamps 600mm apart in a straight line & I...
Replies
9
Views
815
Hello. Please view attached images. I'd like some advice on having the motion sensor control both the light and fan. How should these wires be...
Replies
8
Views
798
On either side of my front door is a motion sensor wall light - it looks like both lights operate from one light switch inside the house. The...
Replies
2
Views
1K
My 4 year old son won't go to bed without the light being left on and insists his door is closed when I leave. When the door is opened later to...
Replies
14
Views
2K
hello all. I am trying to add led strip lights to my boat trailer. I have marine grade submersible lights. I will have them running parallel to...
Replies
3
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock