I have an existing EmerGen Switch installed in my main panel that links to 10 breakers. The main panel is located in the basement.

I recently upgraded my generator and now want to power additional breakers that exist in a sub panel which is located in the garage.

I purchased a second EmerGenSwitch in hopes of hopes of powering additional breakers in the garage from the same generator. Both EmerGen switches use the common neutral and ground. Per code the main panel is bonded and the sub panel is not.

My question is in regard to running generator power to both EmerGen Switches.

the main panel is connected to the sub panel by 2 x 50amp breakers (100 amp sub panel).

My thought was to splice the inbound lead from teh generator and run to both GenSwitches And wire teh gen switches into the proper breakers.

Are there any concerns with wiring the generator to both EmerGen Switches using a splice in the Inbound generator line?
 
I have an existing EmerGen Switch installed in my main panel that links to 10 breakers. The main panel is located in the basement.

I recently upgraded my generator and now want to power additional breakers that exist in a sub panel which is located in the garage.

I purchased a second EmerGenSwitch in hopes of hopes of powering additional breakers in the garage from the same generator. Both EmerGen switches use the common neutral and ground. Per code the main panel is bonded and the sub panel is not.

My question is in regard to running generator power to both EmerGen Switches.

the main panel is connected to the sub panel by 2 x 50amp breakers (100 amp sub panel).

My thought was to splice the inbound lead from teh generator and run to both GenSwitches And wire teh gen switches into the proper breakers.

Are there any concerns with wiring the generator to both EmerGen Switches using a splice in the Inbound generator line?
What do you mean when you say your 100 amp sub panel is being fed by two 50 amp breakers. Since it says that you are a DIY then the only thing that I can say is that is a clear violation of the code book.
 
What do you mean when you say your 100 amp sub panel is being fed by two 50 amp breakers. Since it says that you are a DIY then the only thing that I can say is that is a clear violation of the code book.
The main and sub panel were installed by an electrician (not me). The main panel is 400 amp. the main panel has two 50 amp breakers that feed a 100amp sub panel. The wires appear to be 4 guage running from the main to the sub. The main panel is in the basement. The sub panel is in the garage. The main panel is bonded. The sub panel is not.
 

Reply to Add Second EmerGen Switch to Subpanel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
728
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
858
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
I have hooked up a 30 amp interlock switch to my main panel run off my generator. However, only my light switches work none of my plug-ins have...
Replies
10
Views
742
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock