I am a DIY house renovator. I have 5 outside lights connected to a switch in the hall. Power from the switch goes up the 2 core + earth to the first light, then all of the other 4 lights are daisy chained to each other. (Have 2 cables coming out of each light except the last one) all worked fine no issues.

So i added a new light. Now due to its position on the house, i took the feed coming from light 1 and joined it to the new light 6, and then the feed originally from light one going to light 2, then went from light 6 - now 1,6,2,3,4,5 and not 1,2,3,4,5.

Lights switched on fine and then stay on for about 1.5 hours then RCD snapped?

What have I done? Was convinced this was absolutely the correct thing to do.
 
Remove the two altered fittings and check you have not damaged any conductor insulation and look for water ingress. Can you show a couple of pics for the connections when it is daylight. ISOLATE POWER FIRST.
 
Remove the two altered fittings and check you have not damaged any conductor insulation and look for water ingress. Can you show a couple of pics for the connections when it is daylight. ISOLATE POWER FIRST.
Checked all of the connections today and then put all of the lights on. Been on for about 5 hours and had zero trips from RCD. Leaving them over night to see if they trip. Cannot understand this?
 
I think you may have nicked something and you have shifted it so let's hope for the best.
 

Reply to Added additional LED down/up lighter and now RCD trips after about hour? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
876
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
881
I recently installed a new 15amp circuit breaker, and wired a 14-2 gauge wire to a brand new dimmer switch. From the dimmer switch I daisy chain...
Replies
0
Views
775
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock