Discuss Adding a socket to a garage circuit. in the DIY Electrical Advice area at ElectriciansForums.net

voltemort

DIY
Reaction score
1
Hi everyone,

I've got a garage with a circuit that looks like this:

current.png

I believe it's a radial circuit coming out of the MCB with a current rating of 20A. It goes in to a switch containing a 5A fuse (fused spur?). It then has two wires coming from it: one for a bulb, and the other for a socket.

I would like to add another socket in the garage. I'm thinking the simplest way would be to add a junction box before the current socket, and add the new socket from this junction box:

proposed.png


Would this be the best way to do it?

The wiring seems a bit odd with having the bulb wired in to a switch, but then having the garage door connected using the socket. So any advice in general for tidying up the current circuit would be appreciated.

I have some experience with DIY wiring, but I'm not a professional.
 
Seems quite normal if I read it right.

20A feeds the spur, and the live supply continues to the socket. The light comes off the load side of the spur.

You can branch off a radial circuit anywhere… so whatever is easy between a joint box or coming from the back of the socket.
 
Hi everyone,

I've got a garage with a circuit that looks like this:

View attachment 106658

I believe it's a radial circuit coming out of the MCB with a current rating of 20A. It goes in to a switch containing a 5A fuse (fused spur?). It then has two wires coming from it: one for a bulb, and the other for a socket.

I would like to add another socket in the garage. I'm thinking the simplest way would be to add a junction box before the current socket, and add the new socket from this junction box:

View attachment 106659


Would this be the best way to do it?

The wiring seems a bit odd with having the bulb wired in to a switch, but then having the garage door connected using the socket. So any advice in general for tidying up the current circuit would be appreciated.

I have some experience with DIY wiring, but I'm not a professional.

If the sockets are surface mounted, then I would avoid using a junction box and join at the socket if possible.
 
I'm looking recreate a similar setup as shown in this picture:

piping-small.jpg

I'd like to get these three things:

1. The tubing/piping/protector for the wiring.
2. The clips holding the pipe to the wall.
3. The connector connecting the pipe to the top of the socket.

I don't know what I'm searching for to find these three things.

Does anyone know what their correct names are and where I can buy them from?

I'm from the UK.
 
Screwfix was my friend. I believe these are the terms I was looking for:

1. Conduit Tube
2. Spacer Bar Saddles
3. Conduit Adaptor (not sure whether male or female is what I need though)
 
3. Conduit Adaptor (not sure whether male or female is what I need though)
The one in your pic is female, but they are usually interchangeable.
The female version protrudes less into the box than the male, and provides a nice rounded edge for the cables. The male would be used if you were going into a fitting with a 20mm female thread, rather than just a 20mm hole.
 
For item 2, we professionals have been tasked with using metal saddles in case of premature collapse during a fire.

Firefighters can get tangled in copper cables once all the insulation, plastic pipe and saddles have melted away.
 

Reply to Adding a socket to a garage circuit. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
394
Howdy, I'm looking for help with my plan to install an extra internal double socket and an external double waterproof socket to my garage. I...
Replies
0
Views
1K
Hi, I would like to add a new socket in the bedroom. Current room configuration: 3 existing sockets - wiring coming from the bottom (under the...
Replies
1
Views
685
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
651
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock