Search the forum,

Discuss Adding fused spur for bathroom extactor in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi - I'm planning to fit an extractor with timer to a bathroom, switching on with the lights and had bought a fan isolator switch, but reading the Manrose instructions they insist on double pole fused spur with 3A fuse.

I think it will be easiest to fit a switched fuse spur and not bother with the fan isolator - this will be fitted outside the bathroom above the doorway.

Just figuring out the easiest way to fit this in since the extractor needs live and switched live.

Current setup
electrics1.gif


Suggested:

electrics2.gif


I have also seen options that suggest to use a double pole pull switch instead and then only the extractor fan is protected by the fuse - suggestions?
 
Hi - I'm planning to fit an extractor with timer to a bathroom, switching on with the lights and had bought a fan isolator switch, but reading the Manrose instructions they insist on double pole fused spur with 3A fuse.

I think it will be easiest to fit a switched fuse spur and not bother with the fan isolator - this will be fitted outside the bathroom above the doorway.

Just figuring out the easiest way to fit this in since the extractor needs live and switched live.

Current setupView attachment 39711

Suggested:

View attachment 39712

I have also seen options that suggest to use a double pole pull switch instead and then only the extractor fan is protected by the fuse - suggestions?
Dave do you have any electrical experience / qualifications etc it's difficult to tailor an answer if we don't know your knowledge.
 
no qualifications but do the jobs I think I'm capable of and leave more complicated stuff to professionals. Normally can understand if somethings explained in simple terms - TBF I've read a lot of debate about what I'm trying with many questioning the need for the fuse, but since the manufacturer stated it I'd prefer to go that route.
 
They do not ask for a fused spur but do say it should be installed by a qualified electrician.
PUB0347_iss01_ID_Axial_Fan_ECO150.pdf
"In fact they say must.
NOTE: All wiring must comply with current Regulations. This system must be installed by a qualified electrician.
 

Attachments

  • PUB0347_iss01_ID_Axial_Fan_ECO150.pdf
    265.3 KB · Views: 22
Last edited:
it actually says 'must be supervised by a qualified electrician' - and yes a fairly clear warning which I'm sure their legal team insist is put in to stop them getting sued if someone who doesn't know what they're doing injures themselves.

Happy to hear any suggestions if what i suggested is dangerous or incorrect? First thought was to check with people who know best how complicated a job it is, since when I checked the price quoted for wiring up the fan was around £200, and since I've got 2 to do, and it's only electrics needed since roofer is fitting the vent tiles and I'll mount the extractor and fit ducting etc seemed quite steep - but if someone can explain briefly maybe it will make sense.
Thanks for input so far.
 
Isolate the main supply before making any electrical connections. This system should be installed by a qualified electrician. • Whenfittingthroughanexternalwall,anexternalgrillemustbefittedatalltimes. • Fanshouldonlybeinstalledbyfixedwiring,aflexiblecordshouldnotbeused. • Theapplianceisnotintendedforusebyyoungchildrenorinfirmpersonswithout supervision. • Youngchildrenshouldbesupervisedtoensurethattheydonotplaywiththe appliance. • Precautionsmustbetakentoavoidtheback-flowofgasesintotheroomfrom theopenflueofgasorotheropen-fireapplianceswhenmountedinoutside windows or walls.
 
Happy to hear any suggestions if what i suggested is dangerous or incorrect? First thought was to check with people who know best how complicated a job it is, since when I checked the price quoted for wiring up the fan was around £200, and since I've got 2 to do, and it's only electrics needed since roofer is fitting the vent tiles and I'll mount the extractor and fit ducting etc seemed quite steep - but if someone can explain briefly maybe it will make sense.
if a have a problem with my car .do I play with it or get some knows about cars!
 
if a have a problem with my car .do I play with it or get some knows about cars!
Depends on you really doesn't it? I saw a chap paying halfords £10 to change his indicator bulb recently - would you have done it yourself? Is the halfords person 'qualified'?

Thanks for the copy and paste but I've got the correct instructions right in front of me - I have read it.

If this is meant to be a lecture then thanks. But, I've just looked at instructions for fitting some downlights:

This light fitting has been designed and manufactured exclusively for B&Q These instructions on wiring and installation are provided as a guideline to assist you. Some experience of electrical wiring and do-it-yourself is required to install the light fitting. If at any time you are unsure of how to proceed, please consult a qualified electrician.

So I'm safe to do the lights, but not the extractor?
 
Depends on you really doesn't it? I saw a chap paying halfords £10 to change his indicator bulb recently - would you have done it yourself? Is the halfords person 'qualified'?

Thanks for the copy and paste but I've got the correct instructions right in front of me - I have read it.

If this is meant to be a lecture then thanks. But, I've just looked at instructions for fitting some downlights:

This light fitting has been designed and manufactured exclusively for B&Q These instructions on wiring and installation are provided as a guideline to assist you. Some experience of electrical wiring and do-it-yourself is required to install the light fitting. If at any time you are unsure of how to proceed, please consult a qualified electrician.

So I'm safe to do the lights, but not the extractor?
Oxford dictionary " anyone who installs operates electrical equipment is an Electrician"
 
Don't you just love it when you ask a simple polite question and you don't get an answer?
 
Depends on you really doesn't it? I saw a chap paying halfords £10 to change his indicator bulb recently - would you have done it yourself? Is the halfords person 'qualified'?

Thanks for the copy and paste but I've got the correct instructions right in front of me - I have read it.

If this is meant to be a lecture then thanks. But, I've just looked at instructions for fitting some downlights:

This light fitting has been designed and manufactured exclusively for B&Q These instructions on wiring and installation are provided as a guideline to assist you. Some experience of electrical wiring and do-it-yourself is required to install the light fitting. If at any time you are unsure of how to proceed, please consult a qualified electrician.

So I'm safe to do the lights, but not the extractor?

Do the B&Q instructions inform you that all electrical work must be tested and certificated by a competent person in line with the wiring regulations to ensure safety and that work in a bathroom may be legally reportable to building control ?
They write what Diyers want to hear and what sells products.
 
You should be "competent" when undertaking electrical work. Would hardly say you are competent if you need to post on a forum. If I didn't know how to change a lamp in my car I would pay a professional to do it I wouldn't check on a forum. Especially when we are talking about electrics, you may succeed in installing what you want but will it be done to regs and in a safe manner?
 
Sounds like you've made your mind up to do it any way so just be careful, most sparks I know ( wrong or right) dont bother with the fuse , been debated many times as the difference between a 3 amp fuse and 6 amp mcb wouldn' make much difference, they just connect into lights with switch and permanent and neutral through isolator then to fan. Having considered manufactures instructions but took no notice
 
You should be "competent" when undertaking electrical work. Would hardly say you are competent if you need to post on a forum. If I didn't know how to change a lamp in my car I would pay a professional to do it I wouldn't check on a forum. Especially when we are talking about electrics, you may succeed in installing what you want but will it be done to regs and in a safe manner?

TBF - I searched for the answer before asking it, and quite a few 'competent' or 'qualified' people seem to either - say they don't bother with fuse, question if it has any safety value over 6A MCB.

Have you ever needed to ask a question, or check something with anyone - did that make you incompetent? Have you used google, ever? Why would you?

I'm happy to get a professional in if it's clear to me that it's not safe to do it - but only reason I've been told is the instructions saying get a 'qualified electrician', even though similar job (lights not in bathroom) don't say it. So unsafe in both cases? or just when it says it?
As far as talking about car DIY then yes, there's lots I have done before - my brother's a mechanic - so I know what I'm capable of - it's not difficult to assess the situation and decide if you feel confident to tackle something. But as far as this job goes I assume it's incredibly complicated since no one has offered to explain it!
 
Sounds like you've made your mind up to do it any way so just be careful, most sparks I know ( wrong or right) dont bother with the fuse , been debated many times as the difference between a 3 amp fuse and 6 amp mcb wouldn' make much difference, they just connect into lights with switch and permanent and neutral through isolator then to fan. Having considered manufactures instructions but took no notice
Thanks for the clear and honest response!
 
If you aren’t testing your work with a calibrated multi function tester you are as far away from competent as you could possibly be.

Your insurance company will more than likely argue the same.

Your craftsmanship and “gut feel” doesn’t come into it.

TBF - I searched for the answer before asking it, and quite a few 'competent' or 'qualified' people seem to either - say they don't bother with fuse, question if it has any safety value over 6A MCB.

Have you ever needed to ask a question, or check something with anyone - did that make you incompetent? Have you used google, ever? Why would you?

I'm happy to get a professional in if it's clear to me that it's not safe to do it - but only reason I've been told is the instructions saying get a 'qualified electrician', even though similar job (lights not in bathroom) don't say it. So unsafe in both cases? or just when it says it?
As far as talking about car DIY then yes, there's lots I have done before - my brother's a mechanic - so I know what I'm capable of - it's not difficult to assess the situation and decide if you feel confident to tackle something. But as far as this job goes I assume it's incredibly complicated since no one has offered to explain it!
 
Get with the times boys
It’s MFTs all the way:D:D

LoL I spoiled myself this month and bought myself a new Megger tpt320 voltage tester as my 30+ year old Stienel needs a rest.
The Stienel does not need batteries though so it is still in the bag.
 
Regardless of whether a MFT or AVO8 is used, I think we can safely say that nothing like any testing is going to be carried out for this diy job.

Course you are right but its most probably a class 2 plastic fan off a light circuit so realistically what would you expect him or any one to test, no disrespect intended
 
Course you are right but its most probably a class 2 plastic fan off a light circuit so realistically what would you expect him or any one to test, no disrespect intended

The existing circuit for suitability for alteration as well as the required tests for the alterations.
He was also on about adding in a FCU and fan isolator.
 
Just to clear this up - obviously highly skilled task, with specialist equipment needed. What specific qualification/certificates would any prospective electrician doing the job need to have and I'll make sure to check?
 
H
The existing circuit for suitability for alteration as well as the required tests for the alterations.
He was also on about adding in a FCU and fan isolator.

Hes connecting a fan to a light, as long as he is reasonably sensible he will be fine. Sometimes it' easy to be over petantic

And I'm in jamacia and drunk so I shoulnt be doing this so I need to move away from the forum, love you all x
 
Last edited:
Your arguement of if you ever have to look something up make you incompetent is stupid.
Yeh i didnt know how to do a windsor knot.....i googled it..
But that hasnt got the potential to kill me or anyone else. There's a reason people spend years becoming competent at this...
 
Your arguement of if you ever have to look something up make you incompetent is stupid.
Yeh i didnt know how to do a windsor knot.....i googled it..
But that hasnt got the potential to kill me or anyone else. There's a reason people spend years becoming competent at this...
 
Notice some one made the comment that if you knew what you were doing you wouldn't be asking advice on this forum. Does that mean any one who comes on here asking for advice is the same?
 

Reply to Adding fused spur for bathroom extactor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking at instructions for installation for Baumatic BHI300 it requires a 20A Double pole (3mm separation) switched fused spur, I quote pretty...
Replies
3
Views
814
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
9K
Hi all, wonder if someone can help me. I've bought a bathroom extractor and I do have the wiring there already (previous extractor was there) but...
Replies
6
Views
2K
Hi all, I recently bought a new house and I went to check the installation on my garage. There is a double socket and a fused switch (3A) which...
Replies
18
Views
3K
Hi to all, If extractor fan in bathroom is autonomous does it still require isolator switch or usual fused switch will do? It runs of 12v...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock