Discuss adding shower CU in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
57
hi

just wanted to check something,
when adding a seperate shower CU (split tails) from a 80amp or even 100amp main supply the tails feeding the shower CU do they have to now be 25mm? or will 16mm be adequate due to the fixed load of the shower

The seperate shower cu (63amp 30ma RCD) is this again due to the CU supplying one fixed load so no need to be rated at the 100 or 80amp supply fuse

many thanks
 
its ok now have it sorted, 11kw shower will only draw 47.8 amps max so the 63amp rcd is fine.

same for tails supplying shower CU max of 47.8amps so 16mm would be fine. got confused with minimum of 25mm for MAIN TAILS for above 60amp main fuse
 
11kW shower makes a complete mockery of fitting energy saving lamps. how many low energy lamps would it take to recoup the extra, non-essential 3kW in that shower.?
 
if you split the mains tails and the incoming fuse is 80amp your new cu for the shower main switch would have to be 80amp rated 16 mm tails are sufficient
 
11kW shower makes a complete mockery of fitting energy saving lamps. how many low energy lamps would it take to recoup the extra, non-essential 3kW in that shower.?


That 3kw will probably never be used, mostly down to humans having that issue with excessive heat

Anyway, Looking at the manufactures cables inside the average shower I'd say none of them will ever draw anything close to that and manufactures are just playing it safe
 
if you split the mains tails and the incoming fuse is 80amp your new cu for the shower main switch would have to be 80amp rated 16 mm tails are sufficient

so why do all of the shower rcd units come with a 63A rcd/mainswitch doesnt make any sense especially as most shower manufactures state there showers must be connected to at least an 80amp mainswitch also
 
Last edited:
The RCD cannot be used as an OPD, the rating of the RCD is what current it is rated to, you will need still need an MCB along side it in the enclosure? Unless of course it is an RCCB.
 
Yeah that would do it, also if the main fuse is 60/80amps then 16mm tails would be ok, if 100amp then 25mm tails would really be needed dude to CCC ratings.
 
Hey Lenny, reading that reg doesn't make much sense like so many of them, what is it trying to say? I kind of have an idea what its trying to say but not sure lol cheers
 
by backfusing Lenny are you saying that the cable feeding the shower CU (if under 3 meters) is protected by the MCB in the shower CU lets say 40amps for a 8.5KW shower.

i agree reg not very clear
 
Last edited:
Yip! Stick in 10mm tails if you have them.

Seen on a few sites the fire alarm on the mains panels fed directly off the busbar in 1.5/2.5MM cable. 1000Amp supplies to the panel and the like.
 
I think what he is saying is if the feed ie 16mm tails are over 3m from the origin then you will need a KMF switch at the origin of supply.
So if your shower CU is in the airing cupboard or something and over 3m from the origin of supply you will need a isolator/KMF switch.
 

Reply to adding shower CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
859
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock