Discuss Additional protection by means of RCDs in the UK Electrical Forum area at ElectriciansForums.net

Hi,

I'm an electrical apprentice and was just wondering if anyone could explain additional protection using RCD's?

Thanks
Do you have a copy of BS7671 the big yellow book?
Reg 411.3.3 Additional protection
 
Hi mate. Have you tried Google? Lots of knowledge there.
Is there something specific you would like to know and that is why your are asking the forum?
 
Hi mate. Have you tried Google? Lots of knowledge there.
Is there something specific you would like to know and that is why your are asking the forum?
I think the OP is/was just trying to understand the meaning, I could be wrong but that's my take on the question.
 
Worth keeping it at Home for times just like this one
I don't think he means he has his own personal copy. He is an Apprentice, and I take it he means that he has access to a copy at the training centre when he needs it but doesn't personally own a copy.
 
Hi,

I'm an electrical apprentice and was just wondering if anyone could explain additional protection using RCD's?

Thanks
Danny try and get access to the Trainee area, not sure what the criteria is, plenty of knowledgeable people/Mentors there only to willing to help, plus you won't get any mickey taking, however daft the question may seen to you, give it a try.
 
I don't think he means he has his own personal copy. He is an Apprentice, and I take it he means that he has access to a copy at the training centre when he needs it but doesn't personally own a copy.
Yes mate you probably are correct, from catching from some of the replies, that's how I read the situation, I don't use my copy much now I am retired, but reluctant to give it away as I like to have a quite read sometimes, just to exercise my brain once in a while, Red Wine permitting that is.
 
Just a bit of info from the regs.

411.3.3 Additional protection


In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:

(i) socket-outlets with a rated current not exceeding 20 A, and |

(ii) mobile equipment with a current rating not exceeding 32 A for use outdoors.

An exception to (i) is permitted: |

(a) where, other than for an installation in a dwelling, a documented risk assessment determines that the RCD

protection is not necessary, or

(b) for a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular |

item of equipment.

NOTE 1: See also Regulations 314.1(iv) and 531.2.4 concerning the avoidance of unwanted tripping.

NOTE 2: The requirements of Regulation 411.3.3 do not apply to FELV systems according to Regulation 411.7 or reduced low


voltage systems according to Regulation 411.8.

NOTE 3: See Appendix 2, item 10 in respect of risk assessment.



415.1 Additional protection: Residual current devices (RCDs)


415.1.1
The use of RCDs with a rated residual operating current (lAn) not exceeding 30 mA and an operating

time not exceeding 40 ms at a residual current of 5 lAn is recognized in a.c. systems as additional protection in the


event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users.

415.1.2 The use of RCDs is not recognized as a sole means of protection and does not obviate the need to


apply one of the protective measures specified in Sections 411 to 414.
 
Just a bit of info from the regs.

411.3.3 Additional protection


In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:

(i) socket-outlets with a rated current not exceeding 20 A, and |

(ii) mobile equipment with a current rating not exceeding 32 A for use outdoors.

An exception to (i) is permitted: |

(a) where, other than for an installation in a dwelling, a documented risk assessment determines that the RCD

protection is not necessary, or

(b) for a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular |

item of equipment.

NOTE 1: See also Regulations 314.1(iv) and 531.2.4 concerning the avoidance of unwanted tripping.

NOTE 2: The requirements of Regulation 411.3.3 do not apply to FELV systems according to Regulation 411.7 or reduced low


voltage systems according to Regulation 411.8.

NOTE 3: See Appendix 2, item 10 in respect of risk assessment.



415.1 Additional protection: Residual current devices (RCDs)


415.1.1
The use of RCDs with a rated residual operating current (lAn) not exceeding 30 mA and an operating

time not exceeding 40 ms at a residual current of 5 lAn is recognized in a.c. systems as additional protection in the


event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users.

415.1.2 The use of RCDs is not recognized as a sole means of protection and does not obviate the need to


apply one of the protective measures specified in Sections 411 to 414.

Thanks very much, should help a lot mate
 
Danny try and get access to the Trainee area, not sure what the criteria is, plenty of knowledgeable people/Mentors there only to willing to help, plus you won't get any mickey taking, however daft the question may seen to you, give it a try.

Will do matey, cheers
 
regs.aside, the actual purpose of a RCD is to protect against accidental contact ( of a human or animal's body part ) with a live part which for some reason ( e.g. a cut cable ) has become exposed to touch; as different from fault protection whereby a normally non-live part has become live through a fault ( e.g. a live conductor touching or shorting to a metal enclosure. this latter is protected by your fuse/MCB.
 
Hope that wasn't a cut & paste, the IET police are everywhere :)

Yes it was. Have to see the regs as to how many characters I can 'cut & paste' before I get my hands smacked. :)
 
here's a couple of characters you can copy and paste. in fact, they need a good pasting.

220px-Statler_and_Waldorf.jpg
 

Reply to Additional protection by means of RCDs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
358
Hi all, I’m currently doing an electrical installation & maintenance apprenticeship (EAL) and wanted to know what additional qualifications you...
Replies
2
Views
479
Hi, I was looking at my dishwasher and it has this metal plate with these markings. I am confused about the meaning of "10/16A" - does that...
Replies
4
Views
170
Hello sparkles, I have a question in relation to sequencing the RCDs and MCBs in the CU. I called an electrician to come to my house and upgrade...
Replies
7
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
915

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock