Discuss additional RCD protection from old Wylex fuse oard in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
168
My mate has an old wylex board with the push in rewireable fuses; and has asked about fitting an rcd to one circuit (a ring main) that supplies one outside socket (at the mo he's using a plug in portable rcd when using the mower). He does not want a new consumer unit, and i know that rcbo's are not compatible with these old fuseboards so thats not an option; a rcd spur to the outside socket is not an option either because that means taking out the kitchen sink to access the ring where it loops outside. Therefore he wants to protect the whole circuit with an rcd located near the fuseboard.

Could I take one leg of the ring via the rcd and leave the other leg in the fuseboard, or would both legs of the ring need to go through the rcd ?

Thanks
 
Last edited:
Cheapest option would be to find said socket he's plugging his lawn mower into and replace the socket faceplate with an RCD socket.

Why would you only take one leg off the circuit? presumably you'll be installing the RCD at or near the CU ?
 
how you do this is to take both the L and N legs of the RFC out of the fuse and N bar. extend with in line connectors to reach RCD in an enclosure adjacent to the CU. then you feed the RCD from the fuse and the N bar with a couple of bits of 6mm stripped out of some 6mm T/E . you're then responsible for the whole circuit. test and then fill in a MWC
 
Cheapest option would be to find said socket he's plugging his lawn mower into and replace the socket faceplate with an RCD socket.

Why would you only take one leg off the circuit? presumably you'll be installing the RCD at or near the CU ?

That is another way to do it, but he might aswell have the entire circuit protected. Im thinking of adding an rcd into the circuit just after it leaves the fuseboard, just not sure if both ends of the ring need to go through the rcd, or just one. Im assuming the rcd would still operate if just one side of the ring went through it.
 
no..you need both legs and both N's into the RCD or it will trip.
 
how you do this is to take both the L and N legs of the RFC out of the fuse and N bar. extend with in line connectors to reach RCD in an enclosure adjacent to the CU. then you feed the RCD from the fuse and the N bar with a couple of bits of 6mm stripped out of some 6mm T/E . you're then responsible for the whole circuit. test and then fill in a MWC

So you mean feed the supply side of the rcd with a 6mm radial from the fuse and connect the existing two legs of the ring to the load side ? Why couldn't I just divert one leg of the ring via the rcd ? Which im not sure about so this really is why im asking. If only one leg of the ring went via the rcd then would the whole circuit be protected ? or not ? if you see where im coming from !
 
NO. both L and N legs needs to be diverted through the RCD. this is fairly basic if you know how a RCD works.
 
So you mean feed the supply side of the rcd with a 6mm radial from the fuse and connect the existing two legs of the ring to the load side ? Why couldn't I just divert one leg of the ring via the rcd ? Which im not sure about so this really is why im asking. If only one leg of the ring went via the rcd then would the whole circuit be protected ? or not ? if you see where im coming from !
Are you a qualified electrician?
 
An rcd measures any imbalance between line & neutral, so how be the principles that it would trip if rcd was connected to just one leg of the ring. Thanks telectrix for noting it will trip which I take your word for it, just dont see how this is immediately.
 

Reply to additional RCD protection from old Wylex fuse oard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
428
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
309
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
684
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock