Search the forum,

Discuss Advice for a possible job change? in the Commercial Electrical Advice area at ElectriciansForums.net

I worked for a company that built mobile Fuel skids for 3rd world countries. Basically dirty fuel was cleaned through the Process skid and then used to fuel a Diesel Turbine which rotated a generator.

We basically done everything. A spark and Mech was paired up and done the ladder work. Conduits. Spool and large pipe work. Instruments the lot. There’s jobs like these around just got to know what to look for.
 

Reply to Advice for a possible job change? in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock